Page 2 of 2 FirstFirst 12
Results 11 to 18 of 18
Time curves for Siemens ETU745 & 766
    #11
    California
    21
    24 VDC
    I know you got the terminal locations already, but just want to put in that Siemens is very particular about the 24 VDC that is applied to the trip unit. Iv tried using just a basic variable power supply and the trip unit did not power on. I had to obtain their test power supply which puts out a very steady 24 VDC (comparable to normal variable power supply). The representative I talk with told me it is something about wavelength filtering of the 24 VDC.
  2. #12
  3. oarreola's Avatar
    oarreola is offline
    NETA 2
    Junior Member Pro Subscriber
    Michigan
    Quote Originally Posted by AaronCBI View Post
    Do you have a model number of that power supply, I’ve been trying to get a hold of a representative for a week now with no response.
  4. #13
  5. Kalbi_Rob's Avatar
    290
    Yes, that is what I was talking about with DC ripple voltage. Either you have to have a DC Voltage Regulator or a proper Capacitor to filter out the DC ripple to be a pure DC signal. Essentially, you are must completely remove the AC sine wave into a pure DC flat voltage.
    Siemens electronics is very sensitive, and can be damaged if the ripple is too large.
  6. #14
    California
    21
    Part#
    Quote Originally Posted by oarreola View Post
    6EP1332-5BA20
  8. #15
  9. oarreola's Avatar
    oarreola is offline
    NETA 2
    Michigan
    6EP1332-5BA20
    Thanks
  10. #16
    scott
    This is the manual that answers your question, a little late, but good for anybody else:
    https://docs.natlswgr.com/docs/W1000570.pdf
    To disable the ground fault during primary injection testing common 3 phases on the line side, then run current through 2 phases on the load side.
  12. #17
    scott
    What do you use to power up a ETU 776 trip unit out of the cubicle?
    look at the terminal block labeled x8 on the top of the breaker. The ETU 776 need 24v DC to power the trip unit.
    On the x8 terminal block, hook the hot lead 24v to port #3. Hook the neutral lead to port #4
  14. #18
    Jan 2018
    Alternative methods to disable GFP
    Quote Originally Posted by scottbouch View Post
    Install jumpers between contacts 9-10 to disable NGS
    Install jumpers between contacts 11-12 to disable GFP
  1. Helpful tips for testing Siemens SB-EC trip units (SBS circuit breakers)
    Last Post: August 27, 2021, 06:25 AM
  2. LV Breaker time curves calculators
    By Dave32 in forum Electrical Testing Talk
    Last Post: February 4, 2020, 04:04 PM
  3. Siemens 7UM62 Siprotec Relay - Generator Protection
    By balugalou in forum P&C / Relay Testing Talk
    Last Post: October 31, 2017, 11:09 AM
  4. time current curves for fedral pacific circuit breakers
    By Herc8306 in forum Technical Documents
    Last Post: June 11, 2015, 06:52 PM