Results 1 to 10 of 11
XFMR test question - wye-delta TTR
    A wye-delta transformer has a primary line voltage of 7200 V and a secondary line voltage of 480 V. What is the turns ratio?
    Your Answer: 15:1
    Not sure what I did wrong on this question. They are both line voltages so I thought it was a simple division question.
    Washington, DC
    58
    Quote Originally Posted by dbryce89 View Post
    Your Answer: 15:1
    It is not a simple division. You have to pay attention to the Wye and Delta. Any winding that is Wye, you have to use phase to ground voltage. 7200/1.732. Delta windings use phase to phase.
    7200/1.732= 4160ish / 480 = ?
    Sorry Im doing the math in my head and on my cell phone.
    Hope this helps
  5. JtotheJ is offline Junior Member Pro Subscriber
    May 2015
    16
    Your Answer: 15:1
    I did the same thing. Is the first reply right? Anyone?
    Quote Originally Posted by JtotheJ View Post
    First reply is correct. 4160/480=8.66667
    Hope this helps
    Thank you that cleared up this question for me.
    Your Answer: 15:1
    divided 7200/480(square root 3)= 8.66
    thats because its a 3 phase wye-delta, in a delta-wye I would do in 480(square root 3)/208 in a normal commercial transformer which in fact its 4 as most of us know. correct me if I'm wrong.
    Oct 2016
    Your Answer: 15:1
    you need to find the phase voltage on the secondary which is 277 or 480/square root 3
    then do the math ie 7200/277 answer =25.99
    so your ratio is 25.99:1
    Mar 2018
    Your Answer: 15:1
    For a Wye / Delta the formula is Vh(Vx√3)= with the numbers above it should be 8.660
    For a Delta / Delta it's Vh Vx =
  17. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Member Pro Subscriber
    Richmond, VA
    30
    Your Answer: 15:1
    WI | DE
    So, easy way to remember how to perform turns ratio is to start with the acronym WIDE where WI stands for Wye where current is equal between phase and line, and DE stands for Delta where E (electromotive force which also defines voltage) or voltage is equal between phase and line.
    So, on the Wye side of the transformer you need to take the voltage (assume to be phase voltage if not otherwise noted) and divide by square root of 3 (or ~1.73). So the equation is
    (7200V/(sqrt(3))/480V = 4156.9V/480V = 8.66 so the TTR = 8.66:1
    Turns ratio is only taken on single phases of a transformer, so all values need to be reduced to individual line values to represent each single phase. This is also why you see a 12kV/480 delta/wye transformer with voltage values of 12kV - 480Y/277V.
    If for whatever reason you needed to convert current values from phase to line on a Delta Xfmr, then you take phase current and divide by sqrt(3).
  19. Wanderer20001us's Avatar
    Wanderer20001us is offline Junior Member Pro Subscriber
    Michigan
    18
    WI | DE
    Thanks for this memory tool.