    XFMR test question - wye-delta TTR

    A wye-delta transformer has a primary line voltage of 7200 V and a secondary line voltage of 480 V. What is the turns ratio?
    Your Answer: 15:1

    Not sure what I did wrong on this question. They are both line voltages so I thought it was a simple division question.

  2. #2
  3. Join Date
    Sep 2017
    Location
    Washington, DC
    Posts
    39
    Reputation
    Quote Originally Posted by dbryce89 View Post
    A wye-delta transformer has a primary line voltage of 7200 V and a secondary line voltage of 480 V. What is the turns ratio?
    Your Answer: 15:1

    Not sure what I did wrong on this question. They are both line voltages so I thought it was a simple division question.

    It is not a simple division. You have to pay attention to the Wye and Delta. Any winding that is Wye, you have to use phase to ground voltage. 7200/1.732. Delta windings use phase to phase.

    7200/1.732= 4160ish / 480 = ?

    Sorry Iím doing the math in my head and on my cell phone.

    Hope this helps

  4. #3
  5. JtotheJ is offline Junior Member Pro Subscriber
    Join Date
    May 2015
    Posts
    15
    Reputation
    Quote Originally Posted by dbryce89 View Post
    A wye-delta transformer has a primary line voltage of 7200 V and a secondary line voltage of 480 V. What is the turns ratio?
    Your Answer: 15:1

    Not sure what I did wrong on this question. They are both line voltages so I thought it was a simple division question.
    I did the same thing. Is the first reply right? Anyone?

  6. #4
  7. Join Date
    Sep 2017
    Posts
    1
    Reputation
    Quote Originally Posted by JtotheJ View Post
    I did the same thing. Is the first reply right? Anyone?
    First reply is correct. 4160/480=8.66667

  8. #5
  9. Join Date
    Feb 2018
    Posts
    5
    Reputation
    Quote Originally Posted by ElectricalTestTech View Post
    It is not a simple division. You have to pay attention to the Wye and Delta. Any winding that is Wye, you have to use phase to ground voltage. 7200/1.732. Delta windings use phase to phase.

    7200/1.732= 4160ish / 480 = ?

    Sorry Iím doing the math in my head and on my cell phone.

    Hope this helps
    Thank you that cleared up this question for me.

Subscribe

Login or register to leave a reply!




Related Topics

  1. Replies: 3
    Last Post: January 7, 2018, 01:23 AM
  2. Test Question--High Current Injection
    By alexlounsbury in forum NETA Level 3 Exam
    Replies: 5
    Last Post: July 10, 2017, 12:38 PM
  3. Insulation resistance test set question
    By mkennedyShermco in forum NETA Level 4 Exam
    Replies: 1
    Last Post: July 20, 2016, 01:36 PM
  4. Replies: 2
    Last Post: February 2, 2016, 01:35 PM
  5. Replies: 4
    Last Post: January 24, 2015, 01:34 PM

Related Content

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


Help and Support