how to perform winding resistance test on transformer
    please describe step by step guide how to perform winding resistance test on three phase dry type transformer
    Sep 2016
    Quote Originally Posted by mask12900 View Post
    Using a Transformer Winding Resistance tester connect the current leads and Voltage leads across a winding(In a Wye connected transformer it will be A-N,B-N,C-N, for Delta it will be A-B,B-C,C-A) wait for unit to stabilise and record value.
    Delta values should always be measured values x1.732.
  5. wooddy is offline Junior Member
    Jan 2018
    Quote Originally Posted by bmclean View Post
    i usually do test at 10% of rated current and make sure winding temperature is measured so readings can be corrected to manufacters readings
    Jun 2016
    28
    Dry Type Winding resistance
    To tag on to the 10%, I have always heard you shouldn't exceed 10% rated current. Also the Manual for the Vanguard TTR and Winding resistance sets have really good info for dry types with in accessible neutrals and other nonstandard configurations.
    http://www.vanguard-instruments.com/download
    Breeze through and check out the manuals they have, I learned a good bit from them
  9. Kalbi_Rob's Avatar
    Quote Originally Posted by jflan13 View Post
    Xmfr manufacturers typically recommend that the current output
    selected should not exceed about 10% of the rated winding current, because it will cause erroneous readings due to heating of the winding.
    • Always choose the highest current output possible for the expected resistance
    value.
    • Typical ranges are 0.1-10 % of rated winding current
    Here are some slides from RichmondCC:
    http://engineering.richmondcc.edu/Co...nce%20Test.pdf
    Here is the procedure from TestGuy.net for Winding Resistance Testing:
    https://testguy.net/content/276-Tran...ting-Explained
  1. how to perform insulation resistance test on three phase transformer
    By mask12900 in forum Electrical Testing Talk
    Last Post: February 1, 2018, 07:15 PM
  2. Transformer winding resistance, balance ?
    By rgrabis in forum Electrical Testing Talk
    Last Post: January 19, 2018, 11:34 AM
  3. winding resistance tolerance for a transformer test
    By Larry5441 in forum Electrical Testing Talk
    Last Post: June 29, 2015, 04:33 PM
