Results 1 to 6 of 6
Power Factor Testing
    Washington, DC
    58
    Does the pressure in a oil filled transformer matter when power factoring the transformer?
    For some reason, I recall a topic at a NETA conference or Doble conference that mentioned something along the lines of "you should power factor under positive pressure and not a vacuum"...
    This statement could be totally false and I cannot find any literature to back the statement up. Has anyone else heard anything along these lines?
    Dec 2017
    How to Perform Tan Delta Test with Doble 4100 or Omicron Cpc 100 + TD1
    Any one knows how to perform Tan Delta Test on Dry Type Power Transformer of 2000 Kva and how to connect instrument with Transformer bushings please help me out .
    Regards
  5. wooddy is offline Junior Member
    Jan 2018
    8
    cannot do hv power factor test(doble) under vacuum as you run a risk of flashover, pressure should not make a difference other than the moisture content of the dry air or nitrogen or sf6 in a breaker
    Manchester, MI
    Power Factor Pressure
    I'm not aware of anything regarding the pressure of the transformer that would affect power factor results. Power factor is measuring the capacitance of the insulation and has little to do with the internal conditions beyond the bushings.
    Jun 2018
    Quote Originally Posted by Kerry4407 View Post
    Doble always recommends positive nitrogen pressure before powerfactoring xfmrs.
  11. Kalbi_Rob's Avatar
    Kalbi_Rob is offline Member Pro Subscriber
    Richmond, VA
    32
    Quote Originally Posted by Chipperk View Post
    As quoted from Megger "Application guide for power factor testing of power & distribution transformers" and attached to this post for reference:
    "Never perform electrical tests of any kind on a unit under vacuum. Flashovers can occur at voltages as low as 250 volts."
    As quoted from "Transformers: Basics, Maintenance, and Diagnostics"
    "Transformers must not be sampled if there is a negative pressure(vacuum) at the sample valve. If there is a vacuum at the bottom, air will be pulled in when the sample valve is opened. Wait until the pressure gauge reads positive before sampling. Pulling in a volume of air could be disastrous if the transformer is energized."
    Transformers_AG_en_V01.PDF
  1. Understanding power factor is easy when you relate it to beer!
    By veracon0700 in forum NETA Level 2 Exam
    Last Post: 3 Weeks Ago, 09:21 AM
  2. Replies: 9
    Last Post: August 16, 2018, 02:28 PM
  3. Replies: 7
    Last Post: May 28, 2018, 04:21 PM
  4. Power Factor for New Mineral Oil
    Last Post: August 16, 2016, 01:11 PM