Dry Tranformer Turns Ratio

    #1
  1. Join Date
    Nov 2017
    Posts
    6
    Reputation

    Dry Tranformer Turns Ratio

    How much deviation is allowed from the calculated value ( three phase dry transformer Rated voltage 11000 / 415 volts, Rated Power 2000KVA)? Kindly also mention the reference of Standard.

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    306
    Reputation

    TTR standard deviation

    The standard deviation as defined by ANSI/IEEE C57.12.00-2006, Section 9.1 states that results should be within 0.5% of nameplate markings, with rated voltage applied to one winding. The TTR with accuracy of 0.1% is accepted as a referee.

    - Power Equipment Maintenance and Testing, Paul Gill


    ANSI/NETA standards also state that TTR results should be within 0.5%

  4. #3
  5. Join Date
    Jun 2016
    Posts
    28
    Reputation

    TTR

    Quote Originally Posted by shamimkhan View Post
    How much deviation is allowed from the calculated value ( three phase dry transformer Rated voltage 11000 / 415 volts, Rated Power 2000KVA)? Kindly also mention the reference of Standard.
    In the NETA-MTS and ATS under electrical test results it says, "Turns-ratio test results should not deviate more than one-half percent from either the adjacent coils or the calculated ratio." Page 32 for both books.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. Saturation test of a 1500/5 multi-ratio CT
    By Tseppish in forum Electrical Testing Talk
    Replies: 7
    Last Post: February 26, 2019, 10:47 PM
  2. What is the turns ratio?
    By franko26 in forum NETA Level 2 Exam
    Replies: 15
    Last Post: July 10, 2018, 03:41 PM


Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support