Ground fault trips at half of setting

 Jump to latest post
    #1
  1. joenavymctest is offline
    SUBMARINES ONCE!!
    Junior Member
    Join Date
    Oct 2017
    Location
    reno,nv
    Posts
    1
    Reputation

    Ground fault trips at half of setting

    I have a ground fault test that keeps tripping at half of the setting value. The system has one main circuit breaker, with one CT around the neutral. No trip test comes out fine (current in line side of CB, out of load side, into load side of neutral, through CT, and out of line side of CT). Trip test reversing though CT yields have of the setting value (about 217A vice 400A).

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    281
    Reputation
    What is the CT ratio and what is the relay set to? My first thought is polarity but this cant be the case if no trip came out fine. What was neutral to ground megger readings?

  4. #3
  5. ksviveksiddarth is offline
    Be Different and Make the Difference
    Junior Member
    Join Date
    May 2017
    Location
    India
    Posts
    5
    Reputation
    Quote Originally Posted by joenavymctest View Post
    I have a ground fault test that keeps tripping at half of the setting value. The system has one main circuit breaker, with one CT around the neutral. No trip test comes out fine (current in line side of CB, out of load side, into load side of neutral, through CT, and out of line side of CT). Trip test reversing though CT yields have of the setting value (about 217A vice 400A).
    It would be easy to analyse if you could provide a simple sketch of what exactly the connection is..? and are you performing a test using secondary injection kit.?

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    281
    Reputation
    Any verdict on this one? It's been about a week since OP. I agree a sketch would make it easier to analyze the situation.

  8. #5
  9. Relay1's Avatar
    Relay1 is offline
    I use to be disgusted, now I'm just amused!
    Junior Member Pro Subscriber
    Join Date
    Nov 2017
    Location
    Central Texas
    Posts
    11
    Reputation

    Ground or Neutral ?

    Quote Originally Posted by joenavymctest View Post
    I have a ground fault test that keeps tripping at half of the setting value. The system has one main circuit breaker, with one CT around the neutral. No trip test comes out fine (current in line side of CB, out of load side, into load side of neutral, through CT, and out of line side of CT). Trip test reversing though CT yields have of the setting value (about 217A vice 400A).
    You stated this is a ground fault test and it sounds like it is connected as a neutral test. Are these settings the same?

Subscribe

Login or register to leave a reply!


Share this thread



Related Topics

  1. Zone ground fault protection. Blocking and tripping?
    By marvinray in forum NETA Level 4 Exam
    Replies: 3
    Last Post: October 6, 2017, 03:42 PM
  2. Testing ground fault reduced voltage and blocking capability
    By Sanjayo in forum Electrical Testing Talk
    Replies: 5
    Last Post: January 29, 2016, 02:46 PM
  3. A phase-to-ground fault would primarily produce which type of current?
    By trhea@saberpower.com in forum NETA Level 3 Exam
    Replies: 6
    Last Post: January 8, 2016, 11:14 AM
  4. What is ground fault blocking capability?
    By madsenate in forum NETA Level 3 Exam
    Replies: 2
    Last Post: June 23, 2015, 11:03 AM
  5. Ground fault explained with simple light circuit
    By CCooter in forum NETA Level 2 Exam
    Replies: 0
    Last Post: May 5, 2015, 09:56 AM


Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support