Results 1 to 2 of 2
What IEEE level cable terminations should be used?
  1. kenner14's Avatar
    kenner14 is offline Junior Member Pro Subscriber
    denver, Co.
    15
    In a contaminated outdoor live front transformer, what IEEE level cable terminations should be used?
  3. ElectricalTestTech's Avatar
    Affiliate Member
    Pro Subscriber
    Washington, DC
    69
    Quote Originally Posted by kenner14 View Post
    Here may be a few things to help you out. Cable classes fall under IEEE 48. Unfortunately I do not have access to that standard without paying $150. But I found this information from 3M.
    Since I am not a cable splicer, my initial guess would be Class 1. But take a look for yourself.
    Class 1 Termination
    Provides electric stress control for the cable insulation shield
    terminus; provides complete external leakage insulation
    between the cable conductor(s) and ground; and provides a
    seal to the end of the cable against the entrance of the external
    environment and maintains the operating design pressure, if
    any, of the cable system. This class is divided into three types:
    Class 1A: For use on extruded dielectric cable
    Class 1B: For use on laminated dielectric cable
    Class 1C: Expressly for pressure-type cable systems
    Class 2 Termination
    terminus, and provides complete external leakage insulation
    between the cable conductor(s) and ground.
    Class 3 Termination
    terminus.
    Indoor Termination–Dry
    A termination intended for use where it is protected from
    solar radiation and precipitation and not subject to periodic
    condensation, or other excessive humidity (90% RH or more).
    May be installed in air conditioned or heated areas.
    Indoor Termination–Wet
    direct exposure to both solar radiation and precipitation, but is
    subjected to climatic conditions that can cause condensation
    onto the termination surfaces.
    Outdoor Termination
    A termination intended for use where it is not protected from
    direct exposure to either solar radiation or precipitation. These
    are Class 1A, 1B, or 1C terminations. Class 2 terminations may
    also qualify.
  1. Field Testing of Motors, IEEE 43
    By SecondGen in forum NETA Level 3 Exam
    Last Post: December 24, 2021, 03:47 PM
  2. Cable hi-pot withstanding time, why 15 minutes?
    Last Post: April 16, 2019, 06:37 PM
  3. Replies: 2
    Last Post: July 5, 2018, 04:35 PM
  4. Cable fault locating questions
    By adamwilson in forum NETA Level 3 Exam
    Last Post: October 25, 2016, 03:18 PM