Results 1 to 6 of 6
What will each wattmeter indicate?
    Three coils with a resistance of 4 ohms and impedance of 13 ohms each are connected in wye to a 120/208 Volt panel. What will each wattmeter indicate if three single-phase wattmeters are used to measure the power?
    The correct answer is 341W according to my answer sheet but I seem to keep getting 311W and I don't know what Im doing wrong. Any help would be great!
    Quote Originally Posted by Stephen30002 View Post
    how did you come up with 311W? i'm having trouble with this question, not sure where to start.
  5. baldscreen is offline
    Baldy
    Junior Member Pro Subscriber
    Columbus, OH
    I get same as you...
    I get the same answer as you and verified it through calculator on this site: http://www.rapidtables.com/calc/elec...calculator.htm
    Impedance Z = SQRT(4*4 + 13*13) = 8.823 Ohms
    Angle Theta = ATAN (Impedance/Resistance) = ATAN (13/4) = 72.9 degrees
    Total Power VA = V*V/Z = (120 * 120) / 8.823 = 1058.82 VA
    Real Power Watts = Total Power * Cos Theta = 1058.82 * Cos(72.9) = 311 watts
    Beats me how someone got 345 watts.
  7. Allenxu is offline Junior Member Pro Subscriber
    Mar 2015
    Quote Originally Posted by baldscreen View Post
    Impedance should be 13 ohms instead of 8.8
  9. baldscreen is offline
    Baldy
    Columbus, OH
    I stand corrected...more or less.
    Quote Originally Posted by Allenxu View Post
    You are correct on the impedance. I was thinking of it as reactance ohms.
    So, I'll try it again:
    COS(Theta) = (Resistance/Impedance) = 4/13
Name:	cos theta.JPG
    Total Power VA = V*V/Z = (120 * 120) / 13 = 1107.69 VA
    Real Power Watts = Total Power * Cos Theta = 1107.69*4/13 = 340.8 watts
    Closer, but not quite the 345 watts given as the answer.
  11. Lonpadams's Avatar
    Lonpadams is offline Junior Member Pro Subscriber
    Jan 2017
    Maryland
    either luck or ???
    PF = R/Z = 4/13 = 0.3077
    E = I*R , 120 = I*13 , I = 120/13 = 9.23A
    P = I*E , P = 9.23*120 = 1107.7VA
    0.3077(PF) = W/1107.7VA , W = 1107.7*0.3077 = 340.84
    340.84(W)/9.23A = 36.93V
    36.93V/4OHMS = 9.23A
