ATS does not transfer from utility to generator
    #1
  1. Join Date
    Apr 2014
    Location
    United States
    Posts
    42
    Reputation
    Quote Originally Posted by jwdrowe View Post
    An ATS does not transfer from utility to generator. The generator is running and producing voltage. Which of the following is the cause of it not transferring?
    A) The breaker feeding the ATS did not open
    B) battery does not have enough charge to operate the ATS
    C) Frequency of the generator is too low
    D) Service only lost one phase
    Looking for help on this question. These are my thoughts, what do you think?
    A. This could be possible, the question doesn't state if the utility available light is still on or not
    B. Not sure what type of ATS we are dealing with
    C. Question doesn't specify the application but I would think any sync issues would be resolved at the gen switchboard
    D. This would be a cause for transfer, so this answer is probably incorrect
    Thanks in advance.
  2. #2
  3. ElectricalTestTech's Avatar
    ElectricalTestTech is offline NETA Level IV
    Affiliate Member
    Pro Subscriber
    Join Date
    Sep 2017
    Location
    Washington, DC
    Posts
    69
    Reputation
    Quote Originally Posted by cjones09 View Post
    Thanks in advance.
    A) The breaker feeding the ATS did not open ATS is an OPEN TRANSITION transfer, the breaker isn't supposed to open
    B) battery does not have enough charge to operate the ATS Since when do batteries operate an ATS?
    C) Frequency of the generator is too low ATS controllers monitor generator frequency.
    This is probably the correct answer
    D) Service only lost one phase This is a reason to initiate a transfer. This doesn't explain why it didn't transfer
Subscribe
Share this thread
Related Topics
  1. Cleaning Generator Windings
    By sparky2005 in forum NETA Level 3 Exam
    Last Post: December 8, 2021, 03:08 PM
  2. How to transfer NETA to NICET?
    By fuse600 in forum NICET Electrical Power Testing
    Last Post: August 14, 2019, 11:12 AM
  3. When To Conduct Resistance Testing on Utility Feeders?
    By Jrmcritical in forum Electrical Testing Talk
    Last Post: May 14, 2019, 02:31 PM
  4. What would cause a generator to trip on 32R?
    By djohnson18 in forum NETA Level 3 Exam
    Last Post: January 10, 2019, 11:28 AM
Tags for this Thread
Follow us
Explore TestGuy
NETA Certification Training
Help and Support
You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net