    26
    NOTE
    Quote Originally Posted by Vernon View Post
    Usually they are all subtractive polarity as shown in your drawing. My take was that they would be connected so the currents were additive and if you had 1 A out of CT#1 and 1 A from CT#2 you get 2A in the relay. Since they didn't use the term "polarity" I went with the currents adding and not canceling. Connect the polarity marks together so that the secondary currents are in phase (I think that is what I posted). The same polarity might be a correct answer but, yes, both subtractive is how it would usually be. I have never seen an additive polarity CT - it is current in on H1 is current out in X1 as shown in your attachment.
    The relay is looking at the total current in the two feeders and 400 total amps always gives you 5 A secondary. If just feeder one is loaded to 400A you get 5 relay amps. If just feeder 2 is loaded to 400A - you get 5 A in the relay. if you have a balance and 200 A on each feeder then each secondary is sourcing 2.5 amps for a total of 5A. So the CT value in the relay should be set to 400 to 5 because 400 total amps primary always gives you 5 amps secondary just like it would if you just have one feeder. If you had 800 amps you would get 10 amps regardless of the distribution of load between the cables - but the ratio is supposed to be to 5, not 10. If you had one feeder with a 400:5 you would put 400:5 in the relay for the CT ratio and this is the same thing. 400 primary amps gives you 5A. www.cttestset.com
    This is a duplicate of my post in the other thread.
    Thank you. I finally understood the question and could make an educated decision. You are right, If he CT is 400:5 that is what the relay needs to see.
  2. #12
    Apr 2010
    558
    Answer A is close but there is no correct answer. It should be parallel additive with a ratio of 400:5.
    Answer A has been updated to reflect the correct ratio. Thank you.
  4. #13
    Apr 2017
    15
    Parallel CT
    Quote Originally Posted by marvinray View Post
    Two parallel feeder cables with individual 400:5 CT’s per parallel run are connected to one overcurrent relay per phase. The proper connection would be:
    a. Parallel additive with relay set to 800:5
    b. Parallel subtractive with relay set to 800:5
    c. Series additive with relay set to 400:5
    d. Series subtractive with relay set to 400:5
    Please help me solve this question.
    Answer is A, https://ctlsys.com/support/measuring...el-conductors/
  1. When would you most likely use a negative sequence relay?
    By Tseppish in forum NETA Level 3 Exam
    Last Post: October 9, 2018, 04:41 AM
  2. Total XC for capacitors in parallel
    By adamr8223 in forum NETA Level 3 Exam
    Last Post: December 4, 2016, 02:08 AM
  3. Phase Sequence Relay Testing (Tengen XJ3-G)
    By lnides in forum P&C / Relay Testing Talk
    Last Post: May 30, 2016, 03:25 PM
  4. Trip contact operation after relay testing
    By DetroitLions in forum NETA Level 3 Exam
    Last Post: January 30, 2016, 09:16 PM
  5. Calibrating Allen-Bradley 810 oil-filled motor overload relay
    Last Post: June 30, 2015, 08:47 AM