    Quote Originally Posted by ElectricalTestTech View Post
    Just keep in mind, the new structure of the test recognizes which questions continuously get correct answers. The new structure throws out those questions and inputs different ones so the test can continuously change. While it is good to know the questions put up on this forum, do not expect them to be on your test.
    This is an excellent point. It cant be emphasized enough that when taking the practice exam its important to focus on the subject matter rather than the actual question and answer. We are looking into implementing a similar feature that stops showing you questions after answering them correctly a certain number of times. This way users who frequently take exams will continue to see fresh questions in subsequent exams.

  2. #32
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    257
    Reputation
    Quote Originally Posted by ddd675 View Post
    16. Which SCADA communication is only appropriate for short distances?
    a. RS232
    b. RS485
    c. CAT6
    d. Fibre

    Here are the max distances for each:

    RS232 (50 feet)
    RS485 (1220 meters)
    CAT6 (100 meters)
    Fiber (2000 meters)

  4. #33
  5. Join Date
    Feb 2015
    Posts
    1
    Reputation
    Quote Originally Posted by Inglefles897 View Post
    11. Two 1mH inductors are connected in parallel and in series with two 45uF capacitors connected in parallel. What is the total impedance of the circuit?




    How did you come up with 0.41 milliohms? I don't see how to solve this without frequency to calculate reactance, assuming 60hz this is what i got

    1mH = 2x 377 ohms in parallel= 188.50 ohms
    45uF = 2x 58.9 ohms in parallel = 29.45 ohms
    series 188.50 + 29.45 = 217.95 ohms
    help?
    It is 188.50 - 29.45 because they are 180 degrees apart in a 60 HZ system and when connected in series they subtract from each other. When they are in series the formula is Z = XL - XC. In parallel the formula is more complicated and is similar to R1xR2/(R1+R2). In this case it is (XL*-XC)/(XL-XC). This means that as XL-XC approach zero (resonance frequency) that the impedance of the parallel tank circuit will approach infinity at that resonant frequency, but since the reactor and capacitor have watt losses you will never get infinity and real world examples of a wave trap have been 2000 to 10000 ohms at resonant frequency. A wave trap blocks the resonant frequency from getting onto the operating bus and passes the 60 HZ, so a wave trap has to be rated to carry normal line loads. Your series resonant circuits are similar and we call those line tuners in the power line carrier world. As XL-XC approach resonant frequency the two cancel themselves out and it allows your resonant frequency to pass and it blocks your carrier frequency.

    Resonant Frequency equals 1/(2 PI (LC)^.5). I know that this formula is not needed for the above mentioned problem, but it helps you understand why a problem like this may be important and helps you figure out what size capacitor and reactor is needed for a wave trap and line tuner.

    So, the answer to this problem is actually 159.05.

    My old Navy instructors told me that the Smithsonian had a tank circuit ran for decades and only seemed to lose power when they took measurements, but I but that was just an electronic legend, lol.

  6. #34
  7. MartyCoyne is offline Junior Member Pro Subscriber
    Join Date
    May 2018
    Posts
    12
    Reputation

    Wattmeter question

    Three coils with a resistance of 4 ohms and impedance of 13 ohms each are connected in wye to a 120/208 Volt panel. What will each wattmeter indicate if three single-phase wattmeters are used to measure the power?

    Help: What will each wattmeter indicate?

  8. #35
  9. Join Date
    May 2018
    Posts
    25
    Reputation
    Quote Originally Posted by Vernon View Post
    Didn't read all the answers but this one jumped out and just slapped me as very high. I think that if no three phase connection is given one assumes a single phase transformer. If I tell you I am standing here with a 480V to 120V transformer in my hand you would assume one transformer with a turns ratio of 4 to 1 and a primary voltage of 480 volts.

    Ok - so the full load current at 138,000V and 2,500,000 VA is 18.116 A. At 8%Z with a shorted secondary you would multiply that by 12.5 so at rated voltage you have 226.45 amps Isc. But you are only applying 480V so you would get, proportionately, 0.787 AMPS. Generally, if I specify that a transformer is (for example) 10%Z that means that with the secondary shorted it will take 10% of the rated primary voltage to get full load current. www.cttestset.com
    I can follow all the math except where the 12.5 number came from. Can anyone fill me in on what I missed?

  10. #36
  11. Join Date
    May 2018
    Posts
    25
    Reputation
    Quote Originally Posted by Vernon View Post
    Didn't read all the answers but this one jumped out and just slapped me as very high. I think that if no three phase connection is given one assumes a single phase transformer. If I tell you I am standing here with a 480V to 120V transformer in my hand you would assume one transformer with a turns ratio of 4 to 1 and a primary voltage of 480 volts.

    Ok - so the full load current at 138,000V and 2,500,000 VA is 18.116 A. At 8%Z with a shorted secondary you would multiply that by 12.5 so at rated voltage you have 226.45 amps Isc. But you are only applying 480V so you would get, proportionately, 0.787 AMPS. Generally, if I specify that a transformer is (for example) 10%Z that means that with the secondary shorted it will take 10% of the rated primary voltage to get full load current. www.cttestset.com
    I see it now...

    (kVA x 100)/(kV x %Z)


    Therefore,

    (2,500,000VA x 100)/(138,000V x 8) = 226.449A


    But at 480VAC vice 138,000VAC so,

    138,000/480 = 287.5


    So dividing the short-circuit primary amps by the voltage ratio difference:

    226.449A/287.5 = 0.787A

Page 4 of 4 FirstFirst ... 234
Subscribe

Login or register to leave a reply!




Related Topics

  1. Neta 3 Exam pointers and questions
    By Zepold72 in forum NETA Level 3 Exam
    Replies: 13
    Last Post: April 29, 2016, 05:25 PM
  2. Official NETA Level 2 Exam Most Missed Questions, Spring 2000
    By SecondGen in forum NETA Level 2 Exam
    Replies: 6
    Last Post: March 16, 2016, 08:18 PM
  3. New practice questions and circuit breaker quiz now available
    By testguy in forum News and Announcements
    Replies: 1
    Last Post: June 17, 2015, 03:05 PM

Related Content

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support