    Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance
    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A
    first should be 480Y/277 not 277y/480.
    basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
    z= (100/5)= 20
    short circuit = 3007.08*20= 60189
    so i would just go with the closest answer correct? and also they should fix the error on 277Y.
  2. #2
  3. Join Date
    Jan 2015
    Location
    Minnesota
    Posts
    2
    Reputation
    Agreed
    I work it out to the same answer. Seems you did it right and I would go for the closest answer.
    Quote Originally Posted by rasilva View Post
    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A
    z= (100/5)= 20
  4. #3
  5. madMAX's Avatar
    madMAX is offline Seasoned Member
    Join Date
    Dec 2014
    Posts
    57
    Reputation
    The questions clearly states "determine the approximate short circuit current". Go with the closest answer.
  6. #4
  7. Join Date
    May 2016
    Posts
    6
    Reputation
    Quote Originally Posted by madMAX View Post
    yes sir but its wrong wording that what confused 277y/480 doesn't exist, 480y/277 exist
  8. #5
  9. Join Date
    Apr 2017
    Posts
    1
    Reputation
    fault current
    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A
    z= (100/5)= 20
    2500 x 100
    1.732 x .480 x5
    250,000/4.1568= 60,142
  10. #6
  11. Join Date
    Dec 2018
    Location
    Atlanta, GA
    Posts
    26
    Reputation
    Explain the math
    Could someone explain the math a little more in depth? Never mind I was confused in Z, but looking over it again I understand.
Subscribe
Login or register to leave a reply!
Share this thread
Related Topics
  1. Here's why you should always short a CT secondary
    By SecondGen in forum Safety and Arc Flash Talk
    Last Post: May 20, 2018, 07:39 AM
  2. ARC FLash and Short Circuit Coordination Study
    By mask1290 in forum Electrical Testing Talk
    Last Post: June 14, 2017, 08:40 AM
  3. Continuous current rating of a circuit breaker
    By mainmanmerc in forum NETA Level 2 Exam
    Last Post: October 22, 2016, 07:32 PM
  4. Is there a field test for Fuses to determine how they will perform?
    By Machine Gun Kelly in forum Electrical Testing Talk
    Last Post: April 15, 2016, 12:09 PM
  5. time current curves for fedral pacific circuit breakers
    By Herc8306 in forum Electrical Testing Talk
    Last Post: June 11, 2015, 06:52 PM
Related Content
Follow us
Explore TestGuy
NETA Certification Training
NICET Electrical Power Testing
Help and Support