Results 1 to 3 of 3
Why is the Network Protector phase relay tested at 60° angle?
    Oct 2015
    Why is the phase relay tested at 60° angle, as opposed to the 0° master relay test, if I worded that correctly... What exactly is happening at 60°?
  3. ironshovel77 is offline Junior Member Pro Subscriber
    8
    nwp phase angle relay
    Quote Originally Posted by StoneyJ180 View Post
    I believe what testing at a 60 degree angle does is simulate a reverse power condition, which will trip the network protector.
  5. Relay1's Avatar
    Relay1 is offline
    Nov 2017
    Central Texas
    17
    StoneyJ180,
    I hope you have gotten an answer before now! At 0° this would look like normal load current on the system,
    but the 60° shift would be an indication of a single-phase to ground fault. So this would be a fault condition qualifier for the relays response to trip or block operation.