Why is the Network Protector phase relay tested at 60° angle?

    #1
  1. Join Date
    Oct 2015
    Posts
    1
    Reputation

    Why is the Network Protector phase relay tested at 60° angle?

    Why is the phase relay tested at 60° angle, as opposed to the 0° master relay test, if I worded that correctly... What exactly is happening at 60°?

  2. #2
  3. ironshovel77 is offline Junior Member Pro Subscriber
    Join Date
    Jan 2015
    Posts
    8
    Reputation

    nwp phase angle relay

    Quote Originally Posted by StoneyJ180 View Post
    Why is the phase relay tested at 60° angle, as opposed to the 0° master relay test, if I worded that correctly... What exactly is happening at 60°?
    I believe what testing at a 60 degree angle does is simulate a reverse power condition, which will trip the network protector.

  4. #3
  5. Relay1's Avatar
    Relay1 is offline
    I use to be disgusted, now I'm just amused!
    Junior Member
    Join Date
    Nov 2017
    Location
    Central Texas
    Posts
    17
    Reputation

    What exactly is happening at 60°?

    Quote Originally Posted by StoneyJ180 View Post
    Why is the phase relay tested at 60° angle, as opposed to the 0° master relay test, if I worded that correctly... What exactly is happening at 60°?
    StoneyJ180,
    I hope you have gotten an answer before now! At 0° this would look like normal load current on the system,
    but the 60° shift would be an indication of a single-phase to ground fault. So this would be a fault condition qualifier for the relays response to trip or block operation.

Subscribe

Login or register to leave a reply!


Share this thread

Related Topics

  1. What will each wattmeter indicate?
    By Stephen30002 in forum NETA Level 3 Exam
    Replies: 7
    Last Post: January 6, 2021, 10:04 AM
  2. When would you most likely use a negative sequence relay?
    By Tseppish in forum NETA Level 3 Exam
    Replies: 4
    Last Post: October 9, 2018, 04:41 AM
  3. Phase Sequence Relay Testing (Tengen XJ3-G)
    By lnides in forum P&C / Relay Testing Talk
    Replies: 3
    Last Post: May 30, 2016, 03:25 PM
  4. Help understanding 3 phase electrical systems
    By randywright in forum Electrical Testing Talk
    Replies: 5
    Last Post: October 22, 2015, 11:46 AM

Tags for this Thread



Related Content


Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support