    Digitrip 1150 Trip Alarm

    We have a magnum ds with a digitrip 1150+ that is showing "TRIP" on the display. Breaker is closed and carrying load. Can someone help identify what this means?

  2. #2
  3. Join Date
    Mar 2015
    Posts
    33
    Reputation
    I am not sure about this but was thinking if the breaker was recently tested and someone forgot to clear the last fault that the breaker tripped on? This is just a guess as some trip units will show a fault after testing and must be cleared by pressing a button on the trip unit.

  4. #3
  5. Join Date
    Dec 2014
    Posts
    57
    Reputation
    Quote Originally Posted by Kimbo Slice View Post
    the breaker was recently tested and someone forgot to clear the last fault
    +1 to this. you should be able to clear the message by pushing the red reset button.