Calibrating Allen-Bradley 810 oil-filled motor overload relay

    #1
  1. Join Date
    Jan 2015
    Posts
    7
    Reputation

    Calibrating Allen-Bradley 810 oil-filled motor overload relay

    While calibrating an oil-filled motor overload relay (such as an Allen-Bradley 810 or General Electric CR124Y) if you increase the size of the opening at the bottom of the relay you will:

    Your Answer: Increase pickup and time delay


    Can someone help me with this question?

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Allen-Bradley 810 Operating Time Adjustment: Un-less ordered with a specified time delay setting, the relays are set for minimum time delay when shipped. To increase the time delay, remove the piston from the dashpot and decrease the opening of the adjustment valve by rotating its cover counterclockwise.


    Click image for larger version. 

Name:	allen-bradley-adjustment.png 
Views:	62 
Size:	58.5 KB 
ID:	84


    Full manual is attached below, this info comes from page 3.
    Attached Files Attached Files
    Last edited by SecondGen; January 27, 2016 at 06:59 AM.

Subscribe

Share this thread

Related Topics

  1. When would you most likely use a negative sequence relay?
    By Tseppish in forum NETA Level 3 Exam
    Replies: 4
    Last Post: October 9, 2018, 04:41 AM
  2. Testing liquid filled transformers with load break bushings
    By GDerr81 in forum Electrical Testing Talk
    Replies: 2
    Last Post: November 15, 2016, 02:47 AM
  3. Phase Sequence Relay Testing (Tengen XJ3-G)
    By lnides in forum P&C / Relay Testing Talk
    Replies: 3
    Last Post: May 30, 2016, 03:25 PM
  4. Trip contact operation after relay testing
    By DetroitLions in forum NETA Level 3 Exam
    Replies: 0
    Last Post: January 30, 2016, 09:16 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net