    If a current of 30 amps is measured with a 100 amp 3% ammeter, the maximum possible error in terms of actual error is:
    Im having problems calculating these types of questions, could someone help?

  2. #2
  3. Kimbo Slice is offline Member Pro Subscriber
    Join Date
    Mar 2015
    Posts
    35
    Reputation

  4. #3
  5. Join Date
    Apr 2015
    Location
    Milwaukee, WI
    Posts
    7
    Reputation

    Percent Error reply

    For percent error on that device:

    100Amps X 3% = plus or minus 3 from 100 or a range of 97A to 103A when measuring 100A.

    If the error is +/- 3 amps then your 30Amps may be 27A to 33A.

    if the device is listed as a 3% tolerance over all measurement ranges then use 30A X 3% = plus or minus 0.9A or range of 29.1A to 30.9A

  6. #4
  7. Join Date
    Apr 2015
    Posts
    12
    Reputation
    Quote Originally Posted by stuebes View Post
    For percent error on that device:

    100Amps X 3% = plus or minus 3 from 100 or a range of 97A to 103A when measuring 100A.

    If the error is +/- 3 amps then your 30Amps may be 27A to 33A.

    if the device is listed as a 3% tolerance over all measurement ranges then use 30A X 3% = plus or minus 0.9A or range of 29.1A to 30.9A
    The correct way is this. 30/3=10

  8. #5
  9. Join Date
    Jan 2015
    Location
    Minnesota
    Posts
    2
    Reputation

    Percentage error calculation

    What am I missing if I keep coming up with 3.9%?

    If 4000 was the specified value, and 3850 was the measured value, what is the percent error?

  10. #6
  11. patelnipul5 is offline Junior Member Pro Subscriber
    Join Date
    Nov 2015
    Location
    3062 Renard Lane, Saint Charles, Illinois
    Posts
    4
    Reputation

    Percentage error

    Please see below for percentage error calculation.

    Step 1: Calculate the error (Subtract one value from the other)
    Step 2: Divide the error by the specified value (we get a decimal number)
    Step 3: Convert that to a percentage (by multiplying by 100 and adding a % sign)

    % error =((Specified value-Measured value)/ Specified value )X 100 %

    = ((4000-3850)/ 4000) X 100 %

    = 0.0375 X 100 %
    = 3.75%

  12. #7
  13. Join Date
    Jan 2017
    Posts
    26
    Reputation
    Quote Originally Posted by Flashman View Post
    What am I missing if I keep coming up with 3.9%?

    If 4000 was the specified value, and 3850 was the measured value, what is the percent error?
    I always do
    [expected (specified) - Calculated (Measured)] / expected (specified)

    this will give you a decimal, which can be converted into a percentage by multiplying by 100

  14. #8
  15. simmonmw71 is offline Junior Member Pro Subscriber
    Join Date
    Oct 2017
    Location
    Comanche, TX
    Posts
    1
    Reputation
    Quote Originally Posted by Mmfz85 View Post
    The correct way is this. 30/3=10
    The correct way is;
    2% of 100 is 2.
    2 is the maximum error.
    2/30 is 0.0667 which is 6.6%

Subscribe

Login or register to leave a reply!