Purpose of Megger Guard Terminal
    Jun 2015
    9
    What is the purpose of the Guard terminal on a Megohmeter?
    When testing at higher voltages, such as with cable or transformers, the guard terminal can be used to divert surface leakage from the measuring circuit. For example, if you were performing a Primary to Ground test on a transformer you would guard the secondary windings. Not all insulation testers are equipped with a guard terminal.
    26
    megger guard terminal usage
    If you understood that, which is a excellent explanation, you can transport to the Power Factor testing. The guard, for example, GST - Guard Red, is the same idea, divert from the measurement whatever is connected to the red.
    Sep 2019
    RE:
    So does the guard allow voltages to pass through or does it immediately go to ground?
  9. Relay1's Avatar
    Relay1 is offline
    Nov 2017
    Central Texas
    17
    Guard Mode
    Quote Originally Posted by wightywest View Post
    A simple way to look at it is, you have a closed circuit with the current returning to it's source at the test equipment. Depending on how you hooked up the leads from the set, all or sections of the device current (Leakage) will be measured. The ground lead is just another path back to the test set whether you measure it or not.
  1. Help me understand how a megger works
    Last Post: April 23, 2016, 11:35 AM
  2. Megger MIT Driver Installation Procedure (Windows 7)
    By SecondGen in forum Technical Documents
    Last Post: January 29, 2016, 09:53 AM
  3. Megger Offers Free Testing Tactics Webinar Series
    Last Post: November 1, 2014, 06:00 AM