What is the theoretical maximum symmetrical fault current?
    May 2015
    What is the theoretical maximum symmetrical fault current that would be available at the secondary terminals of a 3-phase 12,470-480Y/277V, 1000kva, 6.25% impedance transformer?
    I am having problems solving this question. Please advise.
    286
    Fault Current = Full Load Amps (FLA) / % Impedance (Z)
    FLA = VA / L-L Voltage x 1.732
    Here is a thread that explains the equations step by step -> http://testguy.net/threads/1341-Easy...-fault-current
    24
    Short-circuit
    Here the information:
    12,470-480Y/277V
    1000kVA, 6.25% impedance
    another way:
    For a impedance of 6.25%, your necessary voltage will be 6.25% of 480 Volts = 30 Volts
    What that means:
    With secondary shorted, if you apply 30 Volts, you will have full transformer current, which is:
ID:	35 (remeber to multiply by 1000 (KVA to VA conversion)
    I = 1202.85 A
    from here you calculate your transformer Impedance
    Z = V/I......Z = 30/1202.85.......Z = 0.025 Ohms.
    Your max short-circuit current:
    I = V/Z.......I = 480/0.025 = 19200 A
    May 2015
    Thanks for the help.
  9. rofo42 is offline Junior Member
    14
    Quote Originally Posted by joaogemal View Post
    12,470-480Y/277V
    another way:
    What that means:
    I = 1202.85 A
    The link that Second Gen posted doesn't state anything about the additional steps you took dealing with the impedance.
    Can anyone confirm?
  11. joelcallow is offline Junior Member Pro Subscriber
    Oct 2015
    Motor winding Results
    Winding test results on a motor indicate possible degradation when the output waveforms show:
    Winding waveform symmetry
    Noticeable difference in winding waveforms
    Chopped waveforms on grounded windings
    Chopped waveforms on phase ungrounded windings
    Having trouble getting an answer for this.
  1. Cable fault locating questions
    By adamwilson in forum NETA Level 3 Exam
    Last Post: October 25, 2016, 03:18 PM
  2. A phase-to-ground fault would primarily produce which type of current?
  3. What is ground fault blocking capability?
  4. Easy way to calculate transformer fault current
    Last Post: June 11, 2015, 06:40 PM
  5. Ground fault explained with simple light circuit
    By CCooter in forum NETA Level 2 Exam
    Last Post: May 5, 2015, 09:56 AM