Results 1 to 10 of 11
what is the AC max use voltage of these gloves?
    Jun 2015
    9
    Class 2 rubber insulating gloves are proof tested at 20000VAC, what is the AC max use voltage of these gloves?
    Mar 2015
    29
    Hope this helps you out
    Voltage protection is broken down into the following classes:
    •Class 00 - Maximum use voltage of 500 volts AC/proof tested to 2500 volts AC
    •Class 0 - Maximum use voltage of 1,000 volts AC/proof tested to 5,000 volts AC
    •Class 1 - Maximum use voltage of 7,500 volts AC/proof tested to 10,000 volts AC
    •Class 2 - Maximum use voltage of 17,000 volts AC/proof tested to 20,000 volts AC
    •Class 3 - Maximum use voltage of 26,500 volts AC/proof tested to 30,000 volts AC
    •Class 4 - Maximum use voltage of 36,000 volts AC/proof tested to 40,000 volts AC
  5. SecondGen's Avatar
    307
    Protective Rubber Equipment Voltage Ratings and Labeling Chart
    Rubber insulating gloves are available in six ASTM defined voltage classes. Rubber insulating sleeves are available in Class 00 through 4. The chart below identifies the class, proof test voltage and maximum allowable exposure voltage for Salisbury Linemen’s Natural Rubber and SALCOR Rubber Protective Equipment.
    • Class 00 (Beige) are proof tested at 2,500 AC / 10,000 DC and have a max use voltage of 500 AC / 750 DC
    • Class 0 (Red) are proof tested at 5,000 AC / 20,000 DC and have a max use voltage of 1,000 AC / 1,500 DC
    • Class 1 (White) are proof tested at 10,000 AC / 40,000 DC and have a max use voltage of 7,500 AC / 11,250 DC
    • Class 2 (Yellow) gloves are proof tested at 20,000 AC / 50,000 DC and have a max use voltage of 17,000 AC / 25,500 DC
    • Class 3 (Green) gloves are proof tested at 30,000 AC / 60,000 DC and have a max use voltage of 26,500 AC / 39,750 DC
    • Class 4 (Orange) gloves are proof tested at 40,000 AC / 70,000 DC and have a max use voltage of 36,000 AC / 54,000 DC
    *Max use voltage when worn with leather protectors.
    Also keep line-to-line voltage in mind when selecting rubber gloves.
    Oct 2014
    18
    Looks like Slice beat me to it! I posted a printable chart here -> http://testguy.net/threads/1464-Prot...Labeling-Chart
    Yes , good chart. The colors are important to know as well.
    This really helped
    if ever in doubt
    you can find all the class specifications in NFPA 70 E.
    Apr 2014
    42
    voltage rated gloves chart
    Don't forget about inspection and testing:
    Gloves and sleeves must be electrically tested before being issued for use. They must also be visually inspected and gloves need to be air tested for any possible defects (for example, cuts, holes, tears, embedded objects, changes in texture) before each day's use and whenever there is a reason to believe they may have been damaged. Best practice is to inspect PPE and air test the gloves and sleeves before each use.
    In addition, the gloves and sleeves must be electrically tested at regular intervals of not more than 6 months for gloves and 12 months for sleeves. When gloves and sleeves are used regularly, best practice is to test as frequently as monthly.
    Rubber blankets are tested annually.
    Jul 2015
    do rubber blankets have the same ratings as rubber gloves?
    Apr 2014
    42
    Rubber blankets follow the same ASTM classifications as gloves and sleeves. The only difference is that blankets aren't required to be color coded.
    Quote Originally Posted by Jimmbo6 View Post
    15
    Google it...or anything else for that matter...
  1. Overpotential test voltage for low-voltage switchgear
    By AlexT90 in forum Electrical Testing Talk