    We have (4) identical EATON 2500kVA transformers equipped with a QUALTROL 118ITM monitor and the cooling fans on one are stuck in the running position, on the secondary side only.

    The transformer is currently in service but some after doing some voltage checks on TB2 at the controller; voltage was found across 5 and 8 but not 1 and 4 which indicates to me that a relay contact is stuck closed somewhere.

    Winding temperatures were well below the set point, somewhere around 40C. We can’t take an outage right now to investigate any further but can someone confirm that we are on the right track with our troubleshooting? Sorry for the cruddy picture, it’s attached for reference.

    Click image for larger version. 

Name:	controller.jpg 
Views:	55 
Size:	80.4 KB 
ID:	19

  2. #2
  3. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    31
    Reputation
    at a glance it looks like you should have power at 3+4 and 7+8 always. When the temp. threshold is met the contacts on 1+4 and 5+8 should close completing your fan circuit and energizing the sets of fans. If you de energize the fan controller and put a ohm meter across 5 + 8 it should read open, if not your internal contacts are stuck shut. my 2 cents

Subscribe

Share this thread

Related Topics

  1. Here's why you should always short a CT secondary
    By SecondGen in forum Safety and Arc Flash Talk
    Replies: 8
    Last Post: January 31, 2021, 10:26 AM
  2. Problem running ratio test with Megger multitap CT test set
    By ejbrewer in forum Electrical Testing Talk
    Replies: 5
    Last Post: June 30, 2016, 03:13 AM
  3. Transformer cooling classifications
    By onebryd2 in forum NETA Level 2 Exam
    Replies: 0
    Last Post: February 9, 2015, 01:39 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net