    Hello,
    I had to perform a Megger insulation resistance test recently on a single phase step voltage regulator and the first part of the procedure had us bond all three bushings together. I canít find a clear explanation as to why all three bushing (Source, Load, and Source Load bushing) need to be bonded together. Red lead (hot) connected to the source bushing and black lead connected to ground. The Megger is set to PI and we run the test for 10 min to saturate the winding fully.
  2. #2
  3. Join Date
    Aug 2015
    Posts
    14
    Reputation
    insulation resitance test
    In a single phase regulator the shunt winding and series windings cannot be isolated so when you energize one of the three bushings, SL, S and L you are energzing the other 2 bushings. Normally you would like to have all of the bushings at the same potential. Since there are no windings to guard or measure between there is one test to ground.
Subscribe
Login or register to leave a reply!
Share this thread
Related Topics
  1. Transformer Insulation Resistance Test Voltages
    By michaellabeit in forum Electrical Testing Talk
    Last Post: April 29, 2022, 04:59 PM
  2. Insulation resistance with PI on a motor
    By Gnollio in forum Electrical Testing Talk
    Last Post: August 13, 2020, 09:56 AM
  3. rotating machinery insulation resistance
    By jwdrowe in forum NETA Level 3 Exam
    Last Post: January 2, 2019, 12:13 PM
  4. Insulation resistance test set question
    By mkennedyShermco in forum NETA Level 4 Exam
    Last Post: June 10, 2018, 12:52 PM
  5. 230kV Auto-Transformer (Insulation Resistance Test)
    By rizza_gay in forum Electrical Testing Talk
    Last Post: January 19, 2018, 11:27 AM
Tags for this Thread
Follow us
Explore TestGuy
NETA Certification Training
NICET Electrical Power Testing
Help and Support