winding resistance tolerance for a transformer test
    Here is a question for you ,what is the winding resistance tolerance for a transformer test and what are you using as a reference for your answer.That was on the level four test.
  3. sepulveda7000 is offline
    NETA IV
    Los Angeles, CA
    transformer winding resistance tolerance
    Quote Originally Posted by Larry5441 View Post
    IEEE 62 Guide for Diagnostic Field Testing of Electric Power Apparatus - Part 1: Oil Filled Power Transformers, Regulators, and Reactors
    +/-5%
    Quote Originally Posted by sepulveda7000 View Post
    +/-5%
    You need to look at IEEE C57.12.90 it is a updated standard stating that winding resistance readings has no specific standards and will only be used as a reference .
    answer
    Adwell International LTD: If all readings are within one percent of each other then they are acceptable. Keep in mind that the purpose of the test is to test for gross differences between the windings and for opens in the connections.
    Quote Originally Posted by ruel guanzon View Post
    That was not the question ,it ask what was the tolerance differences not the goal of the test
  11. rgrabis is offline Junior Member Pro Subscriber
    Jun 2015
    So that's 5%, 1%, or "no standard" depending on the reference. The goal of the question may be for you to match the standard to the reference. I've also seen 1/2% for factory testing from Megger corp.
  13. SecondGen's Avatar
    496
    According to Megger: The industry standard (factory) permits a maximum difference of 1/2 percent from the average of the three phase windings. Field readings may vary slightly more than this due to the many variables. If all readings are within one percent of each other, then they are acceptable.
    For the source document, see this thread -> http://testguy.net/threads/1497-Tran...stance-balance
  1. Transformer winding resistance, balance ?
    By rgrabis in forum Electrical Testing Talk
    Last Post: January 19, 2018, 11:34 AM
  2. 230kV Auto-Transformer (Insulation Resistance Test)
    Last Post: January 19, 2018, 11:27 AM
  3. winding resistance tester and CPC 100
    Last Post: August 4, 2017, 12:09 PM
  4. winding resistance of power transformers
    By Sanjayo in forum NETA Level 2 Exam
    Last Post: March 27, 2016, 07:13 PM