    Field test procedure for Modified Differential Ground Fault systems

    This guide from Square D is a great piece of reference material for testing modified differential ground fault systems. It includes test procedures for Main-Main, Grounded Wye Configuration; Main-Tie-Main, Grounded Wye, Non-Relayed Tie Configuration; Main-Tie-Main, Grounded Wye, Relay Tied Configuration.

    What you might find particularly helpful are the figures that show your test set and jumper connections. I thought this would be a good reference for experienced techs as well as a good learning tool for those who are still trying to grasp the concept of modified diff ground faults. Just passing it along, download in the attachments...
    Reply to Post • 
    Attached Files Attached Files

  2. #2
  3. Join Date
    Jan 2016
    Posts
    3
    Reputation

    Remove the bonding jumper(s)

    Siemens and GE both say to remove one or both of the bonding jumpers during the test of the MDGF. CH and Schneider do not. Electrically, I would think you would want them intact as it would be a real world situation. Is it possible that two of the largest electrical manufacturers have applied a MDGF wrong? Or perhaps someone out there can explain it to me?

    Thanks!
    Reply to Post • 

  4. #3
  5. Join Date
    Jan 2016
    Posts
    1
    Reputation
    The goal of the test is to ensure the ground fault works when only one source is available. When you are using a primary injection test set current will go through all parallel paths. When you have a single source the current should only return to the neutral of the energized transformer. In order so simulate a single source situation you remove the opposite ground to neutral bond to allow only one path for your primary injection test current to flow through. Feel free to correct me if I am wrong. That is how I understood it after going through the plethora of GE ground fault testing procedures.
    Reply to Post • 

  6. #4
  7. Join Date
    Jan 2015
    Posts
    15
    Reputation
    You can find a lot of info on this topic online. Let me know if you need help and I will forward you some docs.
    Reply to Post • 

  8. #5
  9. Join Date
    Aug 2015
    Posts
    23
    Reputation
    Quote Originally Posted by ovatolin View Post
    You can find a lot of info on this topic online. Let me know if you need help and I will forward you some docs.
    Please post any useful docs you may have on test procedures for ground fault. I like to keep a library on my computer in case I can't get online service in the field. THank You.
    Reply to Post • 

Login or register to leave a reply!



Related Topics

  1. Always test before you touch, use this 3-point test procedure
    By Sanjayo in forum Safety and Arc-Flash Talk
    Replies: 0
    Last Post: July 1, 2016, 04:06 PM
  2. Testing ground fault reduced voltage and blocking capability
    By Sanjayo in forum Electrical Testing Talk
    Replies: 5
    Last Post: January 29, 2016, 01:46 PM
  3. A phase-to-ground fault would primarily produce which type of current?
    By trhea@saberpower.com in forum NETA Level 3 Exam
    Replies: 6
    Last Post: January 8, 2016, 10:14 AM
  4. What is ground fault blocking capability?
    By madsenate in forum Electrical Testing Talk
    Replies: 2
    Last Post: June 23, 2015, 11:03 AM
  5. Ground fault explained with simple light circuit
    By CCooter in forum Electrical Testing Talk
    Replies: 1
    Last Post: May 5, 2015, 10:22 AM

Tags for this Thread

Search TestGuy
   Tag Cloud   Advanced Search
Follow us


Explore TestGuy


NETA Certification Training


Help and Support