    Was testing some Nuetral CT's in new gear the other day and I was getting some ratio numbers that were a bit off. Bossman told me to disconnect the ground bound between the neutral and ground buss. I got good numbers after that. Anyone know why I was getting number that were about a 3% difference?
    Reply to Post • 

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III
    Join Date
    Jan 2014
    Location
    United States
    Posts
    163
    Reputation
    How did you have your test leads setup? Its possible that the current on the neutral bus was splitting depending on your configuration. This could cause your secondary current to be less than expected because not all the test current is flowing through the CT.
    Reply to Post • 

  4. #3
  5. Join Date
    May 2017
    Posts
    3
    Reputation
    Quote Originally Posted by bwillsey88 View Post
    Was testing some Nuetral CT's in new gear the other day and I was getting some ratio numbers that were a bit off. Bossman told me to disconnect the ground bound between the neutral and ground buss. I got good numbers after that. Anyone know why I was getting number that were about a 3% difference?
    The connection may have resulted in stray current flowing through the CT.

    www.cttestset.com
    Reply to Post • 

Login or register to leave a reply!



Related Topics

  1. How to Size Transformer Neutral Resistor
    By AlexT90 in forum NETA Level 3 Exam
    Replies: 3
    Last Post: April 12, 2016, 03:04 PM
  2. Zig–Zag Transformers for System Neutral
    By Biscuit in forum Electrical Testing Talk
    Replies: 0
    Last Post: December 5, 2014, 02:51 PM

Tags for this Thread

Search TestGuy
   Tag Cloud   Advanced Search
Follow us


Explore TestGuy


NETA Certification Training


Help and Support