    Contact resistance test producing CT secondary current

    I have a utility customer that experienced a differential trip on an extremely sensitive scheme from a contractor performing a Contact Resistance test on an out of service, but un-isolated breaker.

    The theory is pretty simple. The test set is plugged into 120vac, uses either a half or full wave rectifier to convert to DC. That rectification isn't perfect, especially the half wave. It allows enough AC ripple, or trash, that a small current is induced in the CT.

    My problem is that he needs a peer reviewed article to submit to management. Is anyone aware of a white paper or technical manual that states this? My next step is to hook a spare CT up to a relay for a waveform capture while running Ductor leads through it.
    Reply to Post • 

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III
    Join Date
    Jan 2014
    Location
    United States
    Posts
    163
    Reputation
    How did they test the breaker? I am assuming it was connected in normal position with line bus de-energized and contact-resistance was measured from line bus to load bus.

    As far as finding a peer reviewed article is concerned, I don't know of any but I can ask some relay guys if they have ever seen anything like what your describing. You might be able to contact the manufacturer of the test set for an answer. Your experiment sounds interesting and I would love to see the result.
    Reply to Post • 

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III
    Join Date
    Jan 2014
    Location
    United States
    Posts
    163
    Reputation
    So after talking with some of the guys at my shop, everyone seems to agree that your theory is plausible but more information is needed about the scheme to know what really happened. It's also possible that there is a wiring problem somewhere which caused the breaker to trip.

    Can you provide a sketch of the differential protection scheme along with relay settings and the location of the DLRO test leads? This will help to better understand the various zones of protection.
    Reply to Post • 

  6. #4
  7. Join Date
    Apr 2017
    Posts
    7
    Reputation

    Differential Trip

    Quote Originally Posted by alexlounsbury View Post
    I have a utility customer that experienced a differential trip on an extremely sensitive scheme from a contractor performing a Contact Resistance test on an out of service, but un-isolated breaker.

    The theory is pretty simple. The test set is plugged into 120vac, uses either a half or full wave rectifier to convert to DC. That rectification isn't perfect, especially the half wave. It allows enough AC ripple, or trash, that a small current is induced in the CT.

    My problem is that he needs a peer reviewed article to submit to management. Is anyone aware of a white paper or technical manual that states this? My next step is to hook a spare CT up to a relay for a waveform capture while running Ductor leads through it.
    Review your SLD, check the Zone of protection what equipment are associated with the differential scheme.
    Reply to Post • 

Login or register to leave a reply!



Related Topics

  1. Replies: 5
    Last Post: November 18, 2016, 09:36 AM
  2. Replies: 11
    Last Post: March 31, 2016, 02:26 PM
  3. Contact resistance tester doesn't display any reading
    By lnides in forum Electrical Testing Talk
    Replies: 7
    Last Post: February 2, 2016, 10:53 PM
  4. Important tip for measuring secondary current with AEMC PEL data logger
    By SecondGen in forum Electrical Testing Talk
    Replies: 0
    Last Post: October 8, 2015, 12:19 PM
  5. Expected contact resistance measurement based on breaker frame size
    By SecondGen in forum Electrical Testing Talk
    Replies: 4
    Last Post: July 6, 2015, 09:05 PM

Tags for this Thread

Search TestGuy
   Tag Cloud   Advanced Search
Follow us


Explore TestGuy


NETA Certification Training


Help and Support