Test Question--High Current Injection

    #1
  1. Join Date
    Apr 2014
    Location
    Houston TX
    Posts
    10
    Reputation

    Test Question--High Current Injection

    I disagree that my answer was wrong. The question:

    7. To test the long time delay function of a breaker which is set for 1000 amps ___________ test current is needed.
    From memory answers were:
    a. 1000A
    b. 1500A
    c. 3000A
    d. Need more information

    I chose D, because both B and C could be correct. I also wondered if it was a trick question with the wording. LTD is set in time, they don't specify that 1000 amps is the LT pickup. My answer was marked wrong. If LTD was always to be tested at 3x, then we wouldn't need TCC's, just a standard range. I've tested a 4000a breaker at 8000 to keep a test set from overheating. It would take a lot of time, but I could test the long time function of a 1000a pickup at 1500 amps.

    I dislike that in some questions, tricks are tricks, yet in others, the generic standard seems to be the right answer.

    Anyone else stumble on this?
    Reply to Post • 

  2. #2
  3. Join Date
    Jan 2016
    Posts
    1
    Reputation

    It would be C

    You could test the pickup value at 1000, but the question ask for time delay which would be 3x the rated current which would be the answer C, 3000.
    Reply to Post • 

  4. #3
  5. Join Date
    Apr 2014
    Location
    Houston TX
    Posts
    10
    Reputation
    Quote Originally Posted by Mcfly89 View Post
    You could test the pickup value at 1000, but the question ask for time delay which would be 3x the rated current which would be the answer C, 3000.
    You could test the time delay at 3x. You could also test it at 1.5x, 6x, 10x... We have TCC's to chart every level of current flow, 3x is just a standard that's been used for convenience. NETA doesn't require 3x, nor does any other governing body that I've seen.

    Just because a practice is common doesn't mean it's a rule.
    Reply to Post • 

  6. #4
  7. Larry5443's Avatar
    Larry5443 is offline
    Cabinet Rat Neta Level 4
    Junior Member
    Join Date
    Apr 2014
    Posts
    17
    Reputation
    Quote Originally Posted by alexlounsbury View Post
    You could test the time delay at 3x. You could also test it at 1.5x, 6x, 10x... We have TCC's to chart every level of current flow, 3x is just a standard that's been used for convenience. NETA doesn't require 3x, nor does any other governing body that I've seen.

    Just because a practice is common doesn't mean it's a rule.
    This was talked about at the Neta conference and it was agreed that there is no standard for this type of question.
    Reply to Post • 

  8. #5
  9. Join Date
    Apr 2017
    Posts
    8
    Reputation

    Circuit Breaker Primary Injection

    Quote Originally Posted by alexlounsbury View Post
    I disagree that my answer was wrong. The question:

    7. To test the long time delay function of a breaker which is set for 1000 amps ___________ test current is needed.
    From memory answers were:
    a. 1000A
    b. 1500A
    c. 3000A
    d. Need more information

    I chose D, because both B and C could be correct. I also wondered if it was a trick question with the wording. LTD is set in time, they don't specify that 1000 amps is the LT pickup. My answer was marked wrong. If LTD was always to be tested at 3x, then we wouldn't need TCC's, just a standard range. I've tested a 4000a breaker at 8000 to keep a test set from overheating. It would take a lot of time, but I could test the long time function of a 1000a pickup at 1500 amps.

    I dislike that in some questions, tricks are tricks, yet in others, the generic standard seems to be the right answer.

    Anyone else stumble on this?
    Since you are taking the NETA exam you need to follow as per NETA table 100.7 Inverse Time Trip Test
    at 300% of Rated Continuous Current of Circuit Breakers
    Reply to Post • 

Login or register to leave a reply!



Related Topics

  1. Level III Test Question (Recent 7/16)
    By BRAD2121 in forum NETA Level 3 Exam
    Replies: 2
    Last Post: January 30, 2017, 01:55 PM
  2. How to Test Breaker through Current Injection Tester ?
    By mask1290 in forum Electrical Testing Talk
    Replies: 7
    Last Post: January 24, 2017, 05:38 PM
  3. Insulation resistance test set question
    By mkennedyShermco in forum NETA Level 4 Exam
    Replies: 1
    Last Post: July 20, 2016, 12:36 PM
  4. Looking for high current testing standard for breakers
    By Larry5443 in forum Electrical Testing Talk