New NETA 4 Exam Questions
  1. ddd675 is offline Junior Member
    Jan 2017
    I wrote my NETA 4 test today... and failed. Here are some tips.
    Don't waste your time reading the NETA study material that they give you. I went through it all and did all the Tech Quizzes.... I don't think anything I studied was on the test. NETA updated the exam but didn't update any of the study material. Some of it is outdated and wrong as well.
    The study material focuses on Approach Boundaries, testing levels, expected results, NETA ATS & MTS info etc. NONE OF THIS WAS ON THE EXAM.
    Here are some of the questions I could remember:
    1. What kind of test do you perform on a fibre optic cable?
    a. Time domain reflectometry
    b. Light domain reflectometry
    2. What test value would you use while testing fibre optic cable?
    a. dBs
    3. At what elevation do ohm readings get effected?
    a. 1000m
    4. When testing insulation resistance on a MV Motors, at what voltage does it become ambiguous?
    5. On a main incoming of a 480V switchgear, what class powermeter should be installed?
    a. II
    b. III
    c. IV
    d. V
    6. A DCS is sending an auto speed signal for 30HZ via a 0-20mA transducer. The VFD is only outputting 1-3HZ. The mA measured by a mutimeter at the VFD is 10mA. What is the likely issue?
    a. High resistance in Auto Speed circuit?
    b. AC Component on DC signal
    7. A primary injection is to be performed on a transformer 138kV/25kV, 2500kva, 8%Z using a 480V generator connected to the high side with the low side grounded. The expected current in the high side is?
    8. A harmonic filter bank consists of a capacitor bank at XXuF and XXXmH. Which harmonic is this bank eliminating?
    9. According to ANSI Standards if you can not physically place a lock on a device what extra step needs to be taken to ensure safety.
    10. In insulating oil, what gas would indicate partial discharge in the oil?
    11. Two 1mH inductors are connected in parallel and in series with two 45uF capacitors connected in parallel. What is the total impedance of the circuit?
    12. There is 60 amps measured on the line of a delta transformer secondary. How many amps are in the delta?
    13. Two loads are connected to the same soure. Load 1: 1250KVA @ 0.85PF. Load 2: 600KW, 300KVAR. What is the combined load in KVA & PF.
    14. What is meant by double insulation?
    15. In a 480V solidly grounded system you must _________.
    a. Have automatic ground fault tripping
    b. Not have automatic ground fault tripping
    16. Which SCADA communication is only appropriate for short distances?
    a. RS232
    b. RS485
    c. CAT6
    d. Fibre
    17. A battery bank has batteries where the terminals are bulged and the seals broken. This is likely from:
    a. Improper charging
    b. Increasing plate growth
    c. Decreasing plate growth
    18. Two parallel feeder cables with individual 400:5 CTís per parallel run are connected to one overcurrent relay per phase. The proper connection would be:
    a. Parallel additive with relay set to 800:5
    b. Parallel subtractive with relay set to 800:5
    c. Series additive with relay set to 400:5
    d. Series subtractive with relay set to 400:5
    19. A substation has zone ground fault protection. Which statement is true?
    a. The main will trip before the feeder breakers
    b. The feeder breakers send a block to the main and tie so they donít trip
    c. The feeder breakers send a block the main and tie so they donít trip until their designated tripping time.
    d. The main will trip and block tripping to the other side of the bus
    20. Before using a ground and test device you must perform what test every time before use?
    21. Which statement is true about a DCS System?
    a. Replaces many electromechanical devices
    22. A CT circuit with a CT resistance of 15mohm goes to a SEL-751 (.27VA @ 5A) through 125ft of #12 SIS (.988 ohms per 100ft). What is the appropriate CT class?
    a. C10
    b. C50
    c. C100
    d. C200
    23. What is the IEC 61850 naming structure?
    24. What is true about Natural esters oil?
    a. Cannot be mixed with mineral oil
    b. Has a higher PF than mineral oil
    25. What would a reactor placed at the end of a long transmission line be for?
    26. What is a wavetrap for?
    27. A DC drive with a high carrier frequency could cause issues with
    a. AC ripple
    b. Pulse width modulation
    28. What kind of fault on a transformer is shown on the given waveform?
    a. B to ground internal
    b. Single phase to ground on high side
    29. According to ANSI a newly installed battery bank should be load tested after:
    a. 1 year
    b. 2 years
    c. 4 years
    d. 5 years
    30. Three single phase transformers feed a load and one faults. Connected in open delta how much load can the 2 units support?
    a. 57.7%
    31. While testing a 100KVAR 480V 3 phase wye connected capacitor. What would the expected uF be across A-B terminals.
    Reply to Post •
    Jul 2015
    Legit questions
    Just took it today and passed. These study tips were crucial. Thanks a ton.
    Reply to Post •
    43
    Thanks for the input. Here are some answers
    Please correct me if I'm wrong:
    1.A (Optic time domain reflectometry)
    5.C
    7. You did not specify the xfmr connection but assuming it is Delta/Wye my calculation is 3007.12 A primary
    8. 5th Harmonic
    10. Acetylene
    11. 0.41 miliohms
    12. Not enough info but after assumptions 103.92 A???
    13. 1825.8 @ 0.91 PF
    14. Requires no connection to ground (earth)
    15.B (not required, NEC 700.6(D))
    16.C (most likely since CAT6 length limit is 100 m)
    17.B
    18.A
    19.C
    20. Dielectric withstand @ 75% of Factory acceptance testing value (IEEE C37.20.6)
    22.D (C200 since i came up with a burden of aprox 1.25 ohms which exceed the error limit of a C100)
    24.B (0.89 vs 0.92)
    25 The line reactor compensates for line capacitance, mitigates voltage transients and limits the fault currents. I don't know what the answers were there.
    26. They are used in PLC (Power Line Carrier) to trap the high frequency communication signals typical of 400 Hz
    29.D maybe? (Lead-acid is 5 years and VRLA 12-18 months so we need more info here)
    31. 2.3 micro-farad
    Reply to Post •
    43
    Question 2 correct answer db/km
    Question 14 correct answer is double layer insulation
    Reply to Post •
    43
    Passed my Level 4
    Passed my level 4 yesterday and your questions were very helpful. I will post a couple of the questions as soon as my card is issued (4-6 weeks)
    Thank you very much !
    Reply to Post •
  1. Neta 3 Exam questions
    By Zepold72 in forum NETA Level 3 Exam
    Last Post: November 9, 2016, 11:51 PM
  2. NETA 2: How many exam questions?
    By Clarksalinas in forum NETA Level 2 Exam
    Last Post: April 22, 2016, 06:21 PM
  3. Official NETA Level 2 Exam Most Missed Questions, Spring 2000
    By SecondGen in forum NETA Level 2 Exam
    Last Post: March 16, 2016, 08:18 PM
  4. Replies: 1
    Last Post: June 17, 2015, 03:05 PM