    problem with this calculation see if i am right. or they posted it wrong

    Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance

    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A


    first should be 480Y/277 not 277y/480.

    basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
    z= (100/5)= 20
    short circuit = 3007.08*20= 60189

    so i would just go with the closest answer correct? and also they should fix the error on 277Y.
    Reply • 

  2. #2
  3. Join Date
    Jan 2015
    Location
    Minnesota
    Posts
    2
    Reputation

    Agreed

    I work it out to the same answer. Seems you did it right and I would go for the closest answer.



    Quote Originally Posted by rasilva View Post
    Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance

    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A


    first should be 480Y/277 not 277y/480.

    basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
    z= (100/5)= 20
    short circuit = 3007.08*20= 60189

    so i would just go with the closest answer correct? and also they should fix the error on 277Y.
    Reply • 

  4. #3
  5. Join Date
    Dec 2014
    Posts
    84
    Reputation
    The questions clearly states "determine the approximate short circuit current". Go with the closest answer.
    Reply • 

  6. #4
  7. Join Date
    May 2016
    Posts
    3
    Reputation
    Quote Originally Posted by madMAX View Post
    The questions clearly states "determine the approximate short circuit current". Go with the closest answer.

    yes sir but its wrong wording that what confused 277y/480 doesn't exist, 480y/277 exist
    Reply • 

Login or register to leave a reply!



Related Topics

  1. Output frequency calculation for three-phase alternator
    By mkennedyShermco in forum NETA Level 4 Exam
    Replies: 1
    Last Post: July 21, 2016, 12:33 PM
  2. Problem running ratio test with Megger multitap CT test set
    By ejbrewer in forum Electrical Testing Talk
    Replies: 5
    Last Post: June 30, 2016, 03:13 AM
  3. Percentage error calculation
    By Flashman in forum NETA Level 2 Exam
    Replies: 1
    Last Post: January 8, 2016, 09:04 PM
  4. Having problems with transformer fault current calculation
    By ryan.chapman@emerson.com in forum Electrical Testing Talk
    Replies: 3
    Last Post: June 24, 2015, 09:55 PM
Search TestGuy
   Tag Cloud   Advanced Search
Follow us


Explore TestGuy


NETA Certification Training


Help and Support