Results 1 to 7 of 7
CCVT/CVT Testing
    CCVT/CVT Testing
    Can any of you tell me what test set or method you are using for testing turns ratio on CCVTs? Are you guys applying a high voltage to the high voltage terminal, and measuring the secondary, or are you using a test set? My understanding is a standard TTR test set will record too high of an error due to the voltage decay in the capacitor stack. Vanguard's CTV-765 seems like a simple and fast test set. Any feedback is appreciated. Thanks!
    Reply •
    Dec 2015
    36
    Most simple method I think is using a power factor test set as a power supply to the HV terminal and measure the secondary voltage.
    Reply •
    OH/MI
    32
    totally agree with Sanjayo, just did some a few months back, 80kv-120v I believe. we put 10kv on the high side with our omicron cpc100/td1 and measured 15v on the low side
    Reply •
    Aug 2015
    15
    Could you use an AC hipot if you don't have a power factor set?
    Reply •
    OH/MI
    32
    Quote Originally Posted by randywright View Post
    Never tried that... not sure honestly. I don't see why not.
    Reply •
    Aug 2015
    15
    Hipots usually trip out on very low levels of current.
    Reply •
    OH/MI
    32
    Very true. Yep, not likely you would be able to use a hipot. Good call. Depending on the ratio, I've used just a small power source.
    Reply •