Should I fail this transformer?

    #1
  1. Join Date
    Apr 2014
    Posts
    61
    Reputation

    Should I fail this transformer?

    I am PI testing a small dry type transformer and my reading was 157 gigohm after 10 min but PI is less than 1.

    Neta says investigate valuess less than 100 megohms but PI "shall not be less than 1.0"

    Should I fail this transformer?
    Reply to Post • 

  2. #2
  3. Join Date
    Apr 2015
    Posts
    6
    Reputation
    What size dry type? What was your final value?

    Quote Originally Posted by cjones09 View Post
    I am PI testing a small dry type transformer and my reading was 157 gigohm after 10 min but PI is less than 1.

    Neta says investigate valuess less than 100 megohms but PI "shall not be less than 1.0"

    Should I fail this transformer?
    Reply to Post • 

  4. #3
  5. Join Date
    Apr 2014
    Posts
    61
    Reputation
    225kVA and the final value was 157 gigohm after 10 min.

    Quote Originally Posted by Test Tech from DMV View Post
    What size dry type? What was your final value?
    Reply to Post • 

  6. #4
  7. Join Date
    Apr 2015
    Posts
    6
    Reputation
    I know some megger values decrease when you physically get close to the test leads. 100+ Gig Ohms, I wouldn't fail it.
    Reply to Post • 

  8. #5
  9. Join Date
    Apr 2014
    Posts
    61
    Reputation
    I agree that the value is good but since NETA-ATS specifically says "value shall not be less than 1.0" does that mean it fails no matter what the value is until PI is greater than 1.0? Thanks for the reply.

    Quote Originally Posted by Test Tech from DMV View Post
    I know some megger values decrease when you physically get close to the test leads. 100+ Gig Ohms, I wouldn't fail it.
    Reply to Post • 

  10. #6
  11. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    32
    Reputation
    Did you have the transformer completely isolated?
    Reply to Post • 

  12. #7
  13. Join Date
    Apr 2014
    Posts
    61
    Reputation
    Yes the transformer was isolated. I'm wondering if maybe I have a bad test lead.

    Quote Originally Posted by lester mcmanaway View Post
    Did you have the transformer completely isolated?
    Reply to Post • 

  14. #8
  15. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    32
    Reputation
    Quote Originally Posted by cjones09 View Post
    Yes the transformer was isolated. I'm wondering if maybe I have a bad test lead.
    Do an open air test. The megger should max out pretty much right away
    Reply to Post • 

  16. #9
  17. Zog is offline Junior Member
    Join Date
    Oct 2014
    Posts
    4
    Reputation
    Once you get up in the Gig range the PI ratios are not very important, there is a note somewhere regarding this, I will see if I can find it.
    Reply to Post • 

  18. #10
  19. Join Date
    Apr 2014
    Posts
    61
    Reputation
    So today I re did the test and the problem was not the test leads but the jumper cables I was using to short the windings together. I did the test without the jumpers and the readings went to full scale. Most PI values were well over 4. I've been taught that jumpers help reduce voltage stress on the windings but it clearly has a big effect on the readings.

    Quote Originally Posted by lester mcmanaway View Post
    Do an open air test. The megger should max out pretty much right away
    Reply to Post • 