Results 1 to 8 of 8
Total XC for capacitors in parallel
    Is it just me or is the answer to this is 44.78 ohms? Or am i crazy???
    Three capacitors, a 12 F, a 20 F, and a 30 F, are connected in parallel to a 60 Hz source. The total XC is
    Reply •
    Aug 2015
    23
    Your answer seems to be correct but I got 42.78 ohms when I did the calculation...
    Formula for capacitors in parallel is simply CT = C1 + C2 + C3 and then plug that into XC = 1 / (2 π f C).
    First, find total capacitance...
    CT = 12 F + 20 F + 30 F
    CT = 62 F
    Then find capacitive reactance...
    XC = 1 / (2 π f C)
    XC = 1 / (2 3.141... 60 0.000062) = 42.78 ohms
    Don't forget to use the decimal form for microfarads when calculating capacitive reactance (0.000062 not 62).
    Edit: changed farads from 0.0062 to 0.000062
    Reply •
    OH/MI
    32
    Quote Originally Posted by GavinK5 View Post
    CT = 62 F
    XC = 1 / (2 π f C)
    XC = 1 / (2 3.141... 60 0.0062) = 42.78 ohms
    Don't forget to use the decimal form for microfarads when calculating capacitive reactance (0.0062 not 62).
    microfarad is to the millionth place. 1uF would be .000001. I believe it would be .000062
    Reply •
    Aug 2015
    23
    ah, you are right, not enough zeros in my original equation. post updated. thanks, lester!
    Reply •
    CT = 62 F
    XC = 1 / (2 π f C)
    I fat fingered that. 42.48 is what i got as well
    Reply •
    Nov 2016
    8
    Hi, I have a question
    What is the maximum voltage that can be applied between the terminals of the series combination of 0.1microF,250V and 0.2microF 500V capacitors
    Reply •
  13. SecondGen's Avatar
    NETA Level III
    161
    easily convert electrical units such as microhms to ohms, amps to milliamps, microfarads to farads, etc. -> http://testguy.net/content/210-Metric-Unit-Conversions
    Reply •
    Jun 2016
    Agreed
    Solving for total capacitance and finding reactance is the easiest and best way to prevent math errors. Simple math gives the answer as 42.78 ohms.
    To double check: Find the reactance of each individual capacitor, then find the Rt for the three in parallel. I did it on a non scientific calculator with some quick rounding and came up with an answer of 42.9 ohm, which is close enough for me!
    Reply •
  1. Total burden on current transformer
    By Sanjayo in forum NETA Level 3 Exam
    Last Post: February 19, 2016, 12:50 PM