    SF6 Gas Test NETA Table 100.13

    I've noticed that the moisture criteria of SF6 Gas at NETA Standard is greater than or equal to 200ppm. . .

    Is this correct? or it should be less than or equal to 200ppm...


    Thanks.

    Regards,
    Rizza
    Reply to Post • 

  2. #2
  3. Join Date
    Dec 2015
    Posts
    36
    Reputation
    Name:  neta-table-100-3.jpg
Views: 82
Size:  27.7 KB

    Table says greater than or equal to but also says "per manufacturer," footnote b also says "according to SOME manufacturers." Seems to me this is just a general guideline.