    Easiest method of determining contact sequence

    easiest method of determining contact sequence on LV breaker.
    light circuit
    slow close
    c...
    d...
    I feel like this ones a little misleading. the light circuit is useless unless you slow close the breaker(which is incorrect apparentlly).
    Reply • 

  2. #2
  3. Join Date
    Dec 2015
    Posts
    36
    Reputation
    what is the alternate method if you don't use a light circuit?
    Reply • 

  4. #3
  5. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    32
    Reputation
    Quote Originally Posted by Sanjayo View Post
    what is the alternate method if you don't use a light circuit?
    In our shop we slow close them and use a pin gage set with the arc chutes off to ensure the contacts make within manufacturers spec. (typically an 1/8 as the article reads.) I feel like there is no diffinitive way to tell how much of a variance you have if the lights don't turn on at the exact same time. Its going to be a judgement call that leaves room for error I feel.
    Aside from that how do you use a light circuit if you don't slow close the breaker? I just think they should both be the correct answer if nothing else.
    Reply • 

  6. #4
  7. Join Date
    Dec 2015
    Posts
    36
    Reputation
    Removing the arc-chutes can be a real pain on some models. The procedure you described seems much harder than hooking up a proper light circuit to the primary stabs and doing the simple slow close...
    Reply • 

  8. #5
  9. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    32
    Reputation
    harder but if asked by a customer i'm certain they are correct with my method. But thats kind of besides the point, not really what i was getting at. One of the answers is slow close and one is a light circuit. If slow closing is not a viable method than a light circuit is irrelevant because it would be useless without slow closing the breaker. Regardless of how you measure the touching of the arcing contacts you still have to slow close it to check when the contacts touch. I just think the question needs reworded.
    Reply • 

  10. #6
  11. Join Date
    Dec 2015
    Posts
    36
    Reputation
    No doubt your method is better but the question is which way is easiest. My point is that the slow close doesn't determine the contact sequence, its the act of verifying contact either physically (by looking or measuring) or electrically (using lights).
    Reply • 

  12. #7
  13. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    32
    Reputation
    The light method just does not seem accurate to me. So if you turn the handle on an akr, 1 light lights up move the handle a quarter inch and the second and third lights come on, is that in spec? It would just be a guess really. Im sure its a pretty rare occasion to see the lights come on exactly simultaneously. I feel like even just looking at the contacts with arc chutes off (slow closing) and not even measuring I would have a better chance of telling you if your contacts are in spec than just by guessing if the variance in the lights its ok.
    Reply • 

  14. #8
  15. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    32
    Reputation
    I also hope the arc chutes are coming off anyway during inspection and testing. I was under the impression that was pretty much an industry standard when field testing and cleaning a breaker?

    5 posts
    Reply • 

  16. #9
  17. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III
    Join Date
    Jan 2014
    Location
    United States
    Posts
    161
    Reputation
    Light circuit is used to find out which contact touches first, then you measure the other two, which requires pulling arc-chutes. There should be no more than the 0.032 or whatever manufacturer specifies.

    Quote Originally Posted by Sanjayo View Post
    Removing the arc-chutes can be a real pain on some models. The procedure you described seems much harder than hooking up a proper light circuit to the primary stabs and doing the simple slow close...
    Reply • 

  18. #10
  19. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III
    Join Date
    Jan 2014
    Location
    United States
    Posts
    161
    Reputation
    Quote Originally Posted by lester mcmanaway View Post
    I also hope the arc chutes are coming off anyway during inspection and testing. I was under the impression that was pretty much an industry standard when field testing and cleaning a breaker?
    Related -> http://testguy.net/threads/2758-Do-y...ull-arc-chutes
    Reply • 

Page 1 of 2 12 LastLast

Login or register to leave a reply!



Related Topics

  1. Phase Sequence Relay Testing (Tengen XJ3-G)
    By lnides in forum Electrical Testing Talk
    Replies: 3
    Last Post: May 30, 2016, 03:25 PM
  2. Contact resistance tester doesn't display any reading
    By lnides in forum Electrical Testing Talk
    Replies: 7
    Last Post: February 2, 2016, 10:53 PM
  3. Trip contact operation after relay testing
    By DetroitLions in forum NETA Level 3 Exam
    Replies: 0
    Last Post: January 30, 2016, 08:16 PM
  4. Expected contact resistance measurement based on breaker frame size
    By SecondGen in forum Electrical Testing Talk
    Replies: 4
    Last Post: July 6, 2015, 09:05 PM
  5. Exam question regarding use of a negative sequence relay
    By Tseppish in forum Electrical Testing Talk
    Replies: 0
    Last Post: January 9, 2015, 01:42 PM

Tags for this Thread

Search TestGuy
   Tag Cloud   Advanced Search
Follow us


Explore TestGuy


NETA Certification Training


Help and Support