    Do you always pull circuit breaker arc chutes?

    When maintenance testing breakers how often do you pull the arc chutes to inspect the main contacts? Some guys say you should always pull them, others say its not necessary if contact resistance is good, especially if they are difficult to remove.
    Reply to Post • 

  2. #2
  3. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    32
    Reputation
    Quote Originally Posted by wrh9278 View Post
    When maintenance testing breakers how often do you pull the arc chutes to inspect the main contacts? Some guys say you should always pull them, others say its not necessary if contact resistance is good, especially if they are difficult to remove.
    We do every time just to do a visual inspection. You would not believe how many times we've opened up a breaker and found loose hardware on a contact assembly or a missing contact pad on one of the arcing contacts etc. Im sure it varies upon job scope but i've never been on a job that we did not inspect the contacts.
    Reply to Post • 

  4. #3
  5. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III
    Join Date
    Jan 2014
    Location
    United States
    Posts
    163
    Reputation
    Arc-chutes should always be removed. NETA maintenance specs say you should inspect circuit breaker moving and stationary contacts for condition, wear, and alignment. You should also inspect the individual arc-chutes for damage or signs of excessive arcing.

    If you really want to go by the book you should also verify that primary and secondary contact wipe and other dimensions vital to satisfactory operation of the breaker are correct. These might include sequence and pressure checks.
    Reply to Post • 

  6. #4
  7. Join Date
    Dec 2014
    Posts
    1
    Reputation

    Question to your question

    Quote Originally Posted by wrh9278 View Post
    When maintenance testing breakers how often do you pull the arc chutes to inspect the main contacts? Some guys say you should always pull them, others say its not necessary if contact resistance is good, especially if they are difficult to remove.
    How do you perform a slow close test with out removing the arc shoots? I would refer back to the manual of the breaker, and it will give you step by step on how they would perform their own maintenance
    Reply to Post • 

Login or register to leave a reply!



Related Topics

  1. Identify this circuit breaker symbol
    By MAKI2016 in forum NETA Level 2 Exam
    Replies: 7
    Last Post: 4 Weeks Ago, 03:28 PM
  2. Contact resistance tester doesn't display any reading
    By lnides in forum Electrical Testing Talk
    Replies: 7
    Last Post: February 2, 2016, 10:53 PM
  3. When should circuit breaker contacts be lubricated?
    By zofofg in forum NETA Level 2 Exam
    Replies: 6
    Last Post: July 27, 2015, 09:16 PM
  4. Draw out circuit breaker positions, how many?
    By Mjeelemco in forum NETA Level 2 Exam
    Replies: 3
    Last Post: June 25, 2015, 06:55 PM
  5. Do You Ever Grease Circuit Breaker Contacts?
    By alexlounsbury in forum Electrical Testing Talk
    Replies: 7
    Last Post: May 21, 2014, 06:15 PM

Tags for this Thread

Search TestGuy
   Tag Cloud   Advanced Search
Follow us


Explore TestGuy


NETA Certification Training


Help and Support