Results 1 to 10 of 12
Contact resistance critera/passing range (low voltage air circuit breakers)
  1. rizza_gay's Avatar
    rizza_gay is offline
    TTR Queen
    Jan 2016
    Philippines
    19
    Good Day!
    What is the criteria/passing range and standards for the Contact Resistance Test of Low Voltage Air-Circuit Breaker?
    Specs:
    ABB Manufactured with Iu=1600A, Ue=690V , 3 phase.....
    Among the 4 units I tested for its contact resistance, 3 of it has a higher values. Injected current is 100A AC.
    ACB #1 : 1435 micro ohms ; 1331 ; 847.7
    ACB #2 : 269.6 ; 790 ; 670.8
    ACB #3 : 22.8 ; 22.4 ; 22.3
    ACB #4 : 40.0 ; 39.6 ; 36.5
    Note that all ACB were at the same specs....
    Thank you.
    Godbless.
    Regards,
    Rizza
    Reply •
    Dec 2015
    36
    Greetings Rizza! All three pases should be within 50% of the lowest value.
    Example: 22.3 being lowest value, contacts should not be higher than 33.45 (22.3 x 1.5).
    Reply •
    Jan 2016
    NJ
    18
    at 100 amps...i would give those first two a good cleaning..should drop significantly
    Reply •
  7. rizza_gay's Avatar
    TTR Queen
    Jan 2016
    Philippines
    19
    @Sanjayo
    Thanks a lot. . .
    Is that from NETA standard?
    Regards,
    Rizza
    Reply •
    Dec 2015
    36
    Yes, the +/- 50% rule comes from NETA. Are these new breakers?
    Quote Originally Posted by rizza_gay View Post
    Thanks a lot. . .
    Regards,
    Rizza
    Reply •
  11. rizza_gay's Avatar
    TTR Queen
    Jan 2016
    Philippines
    19
    Hello . . . .
    Thanks a lot. . .
    Regards,
    Rizza
    Yes...those were new ACB. . .
    Reply •
  13. rizza_gay's Avatar
    TTR Queen
    Jan 2016
    Philippines
    19
    Good Day!
    Yup...All breakers were new. One thing I've noticed is that the breakers were in Open Position before I conducted the test. Maybe, the presence of dusts in its contact matters.
    Reply •
    Dec 2015
    36
    What kind of instrument are you using to measure?
    Reply •
  17. rizza_gay's Avatar
    TTR Queen
    Jan 2016
    Philippines
    19
    Its the DV Power CAT66 : Circuit Breaker Analyzer
    Reply •
    Dec 2015
    36
    Did you say this was 100A ac? Using Dc current would give more stable reading.
    Reply •
  1. Expected contact resistance measurement based on breaker frame size
    Last Post: July 6, 2015, 09:05 PM