Determine the approximate short circuit current available
    May 2016
    Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance
    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A
    first should be 480Y/277 not 277y/480.
    basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
    z= (100/5)= 20
    short circuit = 3007.08*20= 60189
    so i would just go with the closest answer correct? and also they should fix the error on 277Y.
    Minnesota
    Agreed
    I work it out to the same answer. Seems you did it right and I would go for the closest answer.
    Quote Originally Posted by rasilva View Post
    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A
    z= (100/5)= 20
  5. madMAX's Avatar
    madMAX is offline Seasoned Member
    57
    The questions clearly states "determine the approximate short circuit current". Go with the closest answer.
    May 2016
    Quote Originally Posted by madMAX View Post
    yes sir but its wrong wording that what confused 277y/480 doesn't exist, 480y/277 exist
    Apr 2017
    fault current
    60,000 A
    54,500 A
    42,000 A
    37,500 A
    25,000 A
    z= (100/5)= 20
    2500 x 100
    1.732 x .480 x5
    250,000/4.1568= 60,142
    Atlanta, GA
    27
    Explain the math
    Could someone explain the math a little more in depth? Never mind I was confused in Z, but looking over it again I understand.
  13. carl21 is offline Junior Member Pro Subscriber
    Feb 2021
    A simple question hopefully
    480 *1.732= 831.36
    why do you multiply 480 by 1.732?
  15. Kalbi_Rob's Avatar
    Quote Originally Posted by carl21 View Post
    480 *1.732= 831.36
    Original equation is for single phase transformer:
    IFLA=(KVA*1000)/EL-L
    To calculate for 3 phase voltage, the square root of 3 (1.732) must be multiplied by the voltage:
    IFLA=(KVA*1000)/(EL-L*1.732)
    EL-L for both of theses transformers is 480V, one is single phase and the other is 3 phase.
  1. Here's why you should always short a CT secondary
    Last Post: January 31, 2021, 10:26 AM
  2. ARC FLash and Short Circuit Coordination Study
    Last Post: June 14, 2017, 08:40 AM
  3. Continuous current rating of a circuit breaker
    By mainmanmerc in forum NETA Level 2 Exam
    Last Post: October 22, 2016, 07:32 PM
  4. Is there a field test for Fuses to determine how they will perform?
    By Machine Gun Kelly in forum Electrical Testing Talk
    Last Post: April 15, 2016, 12:09 PM
  5. time current curves for fedral pacific circuit breakers
    By Herc8306 in forum Technical Documents
    Last Post: June 11, 2015, 06:52 PM