Results 1 to 9 of 9
230kV Auto-Transformer (Insulation Resistance Test)
  1. rizza_gay's Avatar
    rizza_gay is offline
    TTR Queen
    Jan 2016
    Philippines
    19
    What is the proper connections if I'm going to conduct Insulation Resistance Test for the Auto-Transformer?
    For the Primary, Secondary and Tertiary....
    Please.
    Thank you.
    Dec 2015
    38
    HV + IV to Earth
    HV + IV to LV
    LV to Earth
    Hope this helps.
  5. rizza_gay's Avatar
    TTR Queen
    Jan 2016
    Philippines
    19
    Thank you.
    Good day SIr Sanjayo!
    Thanks a lot. . .it really helps.
    God bless. . .
    Warm regards from Philippines. . . .
    Rizza
    Mar 2016
    Can you please tell the specifications of your Auto transformer?
    if you have any image for this and schematic for your system?
    Also where you are installing it and what are the specifications of device with which you are going to install this transformer?
    smt pcb
  9. rizza_gay's Avatar
    TTR Queen
    Jan 2016
    Philippines
    19
    Good Day!
    Good Day Sir Dickie Cornell!
    Actually the transformer is a Three Phase Forced-Air Cooling Autotransformer with OLTC.
    Its rated Power in MVA are:
    HV=37.5 ; LV=37.5 ; TV=11.25
    With rated Voltage in kV are:
    HV=230 ; LV=69 ; TV=13.8
    Manufactured by SEC ALSTOM (Shanghai Baoshan) Transformers Co., Ltd.
    Thank you.
    Dec 2015
    38
    Sounds like you are testing a very large transformer Rizza, I'm also interested in the application. Are you able to post a picture of the transformer?
  13. rizza_gay's Avatar
    TTR Queen
    Jan 2016
    Philippines
    19
    Power Transformer Picture
    Pls. see attached file.
    Thank you.
    Regards,
    Rizza
    Dec 2015
    38
    Looks great rizza! Best of luck to you!
    Quote Originally Posted by rizza_gay View Post
    Thank you.
    Regards,
    Rizza
  17. wooddy is offline Junior Member
    Jan 2018
    8
    Please.
    Thank you.
    there are a couple of options, you can do H1 to Ho, full set of readings, then do one reading from X1 to Xo( this reading will be a constant reading since the tapchanger will be between the H1 and X1 winding, you can then subtract that X1 reading from all of the H1 to Ho readings to just get the H1 to X1 value if needed, as for the tertiary it usualy is a delta so readings would be Y1 to Y2, Y2 to Y3 and Y3 to Y1
  1. Ripple Test of OLTC Auto-Transformer using Omicron CPC-100
    Last Post: March 30, 2016, 09:09 PM
  2. Replies: 6
    Last Post: January 5, 2016, 02:09 PM
  3. winding resistance tolerance for a transformer test
    By Larry5441 in forum Electrical Testing Talk
    Last Post: June 29, 2015, 04:33 PM