    Blocking capability and reduced voltage tripping are two tests listed for ground fault relays in NETA-ATS, can someone explain how these two tests are performed?
    Reply to Post • 

  2. #2
  3. Join Date
    Jul 2015
    Location
    Portland, OR
    Posts
    6
    Reputation
    Reduced voltage is accomplished with reduced control power voltage (we typically use 55%). This simulates what the ground fault control relay would have to function with if one of the legs feeding the control power transformer was grounded.
    The blocking is, i believe, tested to ensure that the switch does not close back in on an active ground fault, or at least on an unacknowledged one.
    Reply to Post • 

  4. #3
  5. Join Date
    Dec 2015
    Posts
    36
    Reputation
    Thanks for the reply. Is this test done with a simple variable voltage source? For example, if I had 120V AC control power, at 55% my AC variable source would be set to 66V, then I would push current through CT and the relay should still trip?

    Quote Originally Posted by alexanderchaney View Post
    Reduced voltage is accomplished with reduced control power voltage (we typically use 55%). This simulates what the ground fault control relay would have to function with if one of the legs feeding the control power transformer was grounded.
    Reply to Post • 

  6. #4
  7. Join Date
    Jul 2015
    Location
    Portland, OR
    Posts
    6
    Reputation
    Yep. Exactly.
    Reply to Post • 

  8. #5
  9. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III
    Join Date
    Jan 2014
    Location
    United States
    Posts
    162
    Reputation
    NETA references zone-interlocking for the blocking capability test. Unless a restraint signal is used, any ground fault relay with zone interlocking will trip instantaneously regardless of the delay setting.

    The restraint signal is normally applied with a small jumper between specified terminals on the ground fault relay -- consult the relay manufacturers literature for this procedure. Perform a time test with and without this signal applied to ensure proper operation.

    Quote Originally Posted by alexanderchaney View Post
    The blocking is, i believe, tested to ensure that the switch does not close back in on an active ground fault, or at least on an unacknowledged one.
    Reply to Post • 

  10. #6
  11. Join Date
    Jul 2015
    Location
    Portland, OR
    Posts
    6
    Reputation
    ahh, thanks for the clarification.
    Reply to Post • 

Login or register to leave a reply!



Related Topics

  1. clamp-on vs. 3 point ground testing?
    By grahmm in forum Electrical Testing Talk
    Replies: 1
    Last Post: October 24, 2016, 06:40 AM
  2. Field test procedure for Modified Differential Ground Fault systems
    By Biscuit in forum Electrical Testing Talk
    Replies: 4
    Last Post: October 22, 2016, 07:42 PM
  3. A phase-to-ground fault would primarily produce which type of current?
    By trhea@saberpower.com in forum NETA Level 3 Exam
    Replies: 6
    Last Post: January 8, 2016, 10:14 AM
  4. What is ground fault blocking capability?
    By madsenate in forum Electrical Testing Talk
    Replies: 2
    Last Post: June 23, 2015, 11:03 AM
  5. Ground fault explained with simple light circuit
    By CCooter in forum Electrical Testing Talk
    Replies: 1
    Last Post: May 5, 2015, 10:22 AM

Tags for this Thread

Search TestGuy
   Tag Cloud   Advanced Search
Follow us


Explore TestGuy


NETA Certification Training


Help and Support