    Blocking capability and reduced voltage tripping are two tests listed for ground fault relays in NETA-ATS, can someone explain how these two tests are performed?
    Reply to Post •
    Jul 2015
    Portland, OR
    Reduced voltage is accomplished with reduced control power voltage (we typically use 55%). This simulates what the ground fault control relay would have to function with if one of the legs feeding the control power transformer was grounded.
    The blocking is, i believe, tested to ensure that the switch does not close back in on an active ground fault, or at least on an unacknowledged one.
    Reply to Post •
    Dec 2015
    39
    Thanks for the reply. Is this test done with a simple variable voltage source? For example, if I had 120V AC control power, at 55% my AC variable source would be set to 66V, then I would push current through CT and the relay should still trip?
    Quote Originally Posted by alexanderchaney View Post
    Reply to Post •
    Jul 2015
    Portland, OR
    Yep. Exactly.
    Reply to Post •
  9. SecondGen's Avatar
    NETA Level III
    163
    NETA references zone-interlocking for the blocking capability test. Unless a restraint signal is used, any ground fault relay with zone interlocking will trip instantaneously regardless of the delay setting.
    The restraint signal is normally applied with a small jumper between specified terminals on the ground fault relay -- consult the relay manufacturers literature for this procedure. Perform a time test with and without this signal applied to ensure proper operation.
    Reply to Post •
    Jul 2015
    Portland, OR
    ahh, thanks for the clarification.
    Reply to Post •
  1. clamp-on vs. 3 point ground testing?
    By grahmm in forum Electrical Testing Talk
    Last Post: October 24, 2016, 06:40 AM
  2. Field test procedure for Modified Differential Ground Fault systems
    By Biscuit in forum Electrical Testing Talk
    Last Post: October 22, 2016, 07:42 PM
  3. A phase-to-ground fault would primarily produce which type of current?
    Last Post: January 8, 2016, 10:14 AM
  4. What is ground fault blocking capability?
    By madsenate in forum Electrical Testing Talk
  5. Ground fault explained with simple light circuit
    By CCooter in forum Electrical Testing Talk
    Last Post: May 5, 2015, 10:22 AM