    Sep 2015
    What determines the continuous current rating of a breaker? My answer is size of the frame but I was told that is incorrect. Can someone explain?
    Reply •
    84
    Frame size does not matter because you can have 1600AF/800AT for example. Think of the main components of the LVCB protection, which pieces are interchangeable?
    Reply •
    Aug 2015
    23
    Any one of these could be the answer > current transformers > trip unit > rating plug > protective settings
    Reply •
    Jan 2016
    Central Indiana
    When we refer to the rating as continuous, Is it 3 hours or more, just like a motor?
    Reply •
    Aug 2015
    23
    Quote Originally Posted by cj65shelby View Post
    Yes, the 3 hour standard comes from NEC. Here is some related info:
    continuous current rating (handle rating) (ampere rating) The designated RMS alternating or direct current in amperes which a device or assembly will carry continuously in free air without tripping or exceeding temperature limits.
    The 1996 NEC recognizes that overcurrent protective devices will be affected by heat in the system. As such, it defines the concept of continuous loads and the 80% rule to try and offset the effects of heat in the system when sizing a CB.
    Continuous loads. To better understand the sizing aspects of a CB, you must first clearly understand the concept of continuous loads. In Art. 100, the NEC defines a continuous load as "a load where the maximum current is expected to continue for three hours or more." It's critical for you to understand that this is a load at its maximum current uninterrupted for at least three hours. Office lighting typically meets this qualification.
    http://testguy.net/content/150-Circu...current_rating
    http://ecmweb.com/basics/sizing-circuit-breaker
    Reply •
  1. Identify this circuit breaker symbol
    Last Post: January 5, 2017, 12:45 PM
  2. Contact resistance tester doesn't display any reading
    Last Post: February 2, 2016, 10:53 PM
  3. When should circuit breaker contacts be lubricated?
    By zofofg in forum NETA Level 2 Exam
    Last Post: July 27, 2015, 09:16 PM
  4. Do You Ever Grease Circuit Breaker Contacts?
    By alexlounsbury in forum Electrical Testing Talk
    Last Post: May 21, 2014, 06:15 PM