What methods do you use for corona suppression when testing cable?

    #1
  1. Join Date
    Dec 2014
    Posts
    84
    Reputation

    What methods do you use for corona suppression when testing cable?

    This may be going overboard but for the test end I like to tape my lead to the conductor with some rubber splicing tape, wrap that with 33, and wrap all of that with plastic wrap. Opposite ends will usually just get plastic wrap and a PVC boot (made from piece of 18" PVC pipe and cap). With this method I get no hissing even with high humidity. Anyone have similar methods to suppress corona when testing cable?
    Reply to Post • 

  2. #2
  3. Join Date
    Aug 2015
    Posts
    15
    Reputation
    Splice tape is usually good enough unless you are testing at crazy high voltages. Rubber safety blankets are also very useful when testing cable.
    Reply to Post • 

  4. #3
  5. Join Date
    Dec 2016
    Location
    Edmonton, AB
    Posts
    3
    Reputation
    depending on test set our VLF/TD units minus the TD28 have corona Balls otherwise its wrap the lug tightly in the thicker Danger Tape and a little electrical tape to hold it in place then toss a rubber insulating boot over that does a good job but is not perfect, also less expensive then using splicing tape.
    Reply to Post • 

  6. #4
  7. Join Date
    Dec 2014
    Posts
    84
    Reputation
    Corona Balls? Sounds like you got that fancy stuff, Alex. My company only provides the bare essentials. Using rubber boots and blankets seems like a good idea except large blankets can be a pain to work with. Maybe I can rob some boots if I come across some on a job. The insulating plastic I have is only good for 8kV I think.
    Reply to Post • 

  8. #5
  9. Join Date
    Apr 2014
    Location
    Houston TX
    Posts
    10
    Reputation
    During VLF testing, I haven't found a need to cover the cables. The theory behind the practice is just to limit the amount of air moving across the cables.

    For DC HiPot, keep in mind it's a pass/fail test. I used to work hard for high quality corona supression, but even a high reading shouldn't be used for trending. If it holds the voltage, it passes. Leakage currents will vary widely with humidity and wind, regardless of the supression method. Also worth noting that any direct contact that the insulation method makes will create a point for leakage current.

    In a pinch several years ago, I used latex gloves. They worked great, though I wouldn't recommend them as a general practice.
    Reply to Post • 

Login or register to leave a reply!



Related Topics

  1. Cable hi-pot step voltage test
    By cjones09 in forum Electrical Testing Talk
    Replies: 1
    Last Post: August 25, 2015, 06:38 AM
  2. Cable Insulation Precentage
    By CanTest in forum Electrical Testing Talk
    Replies: 1
    Last Post: June 24, 2014, 04:21 PM

Related Content

Tags for this Thread

Search TestGuy
   Tag Cloud   Advanced Search
Follow us


Explore TestGuy


NETA Certification Training


Help and Support