    winding resistance tester and CPC 100

    Hi, everyone. I used a winding resistance tester to test 0.75 MVA transformer primary (13800-600). I got a unbalance phase resistance. H1-H2 WAS 2.6om AND H1-H3 WAS 3.8OM. H2-H3 WAS 8.7OM.

    I DON'T THINK SOMETHING WRONG WITH THE TX, IT IS ACCEPTANCE TEST. I USED CPC-100 TO TEST TX AGAIN. I GOT EVERY PHASE WERE AROUND 2.6OM.

    I THINK THE REASON FOR WINDING RESISTANCE IS THAT I DID NOT DISCHARGE THE TX AFTER H1-H2 TESTING AND STARTED TO TEST H1-H3 IMMEDIATELY. BUT THE CPC-100 DISCHARGE THE TX AUTOMATICALLY.

    JUST REMIND TO DISCHARGE THE TX AFTER TEST.
    Reply to Post • 

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III
    Join Date
    Jan 2014
    Location
    United States
    Posts
    162
    Reputation
    hmm...this is an interesting scenario, it almost seems like you had two or more wingdings in series by accident? I don't see how discharging the transformer would have made that big of a difference. How long did you apply current before taking your readings? I would be interested to know more about which test set you were using and how you had the leads connected.
    Reply to Post • 

  4. #3
  5. Join Date
    Jun 2015
    Posts
    7
    Reputation

    discharge the TX

    First, used the AEMC 6240 10A Micro-Ohmmeter. It need five minutes to get stable.

    Then use omicron CPC 100. pretty quick to get stable. and CPC automatically discharage the TX. The TX is wye to Delta. I tested the high sigh. impossible to series two winding.
    Reply to Post • 

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III
    Join Date
    Jan 2014
    Location
    United States
    Posts
    162
    Reputation
    The fact that you were using a 10A ductor is probably why your readings were funky. Was it battery powered? If the batteries were low you wont get accurate readings because the current is not stable, especially if you are pushing current for 5 minutes. Using a test set that operates off of utility supplied AC like the Omicron CPC 100 is a much better method. Putting two windings in series was a long shot, I know, I was just brainstorming.

    Quote Originally Posted by moon1958moon View Post
    First, used the AEMC 6240 10A Micro-Ohmmeter.
    It need five minutes to get stable.
    Then use omicron CPC 100. pretty quick to get stable. and CPC automatically discharage the TX. The TX is wye to Delta. I tested the high sigh. impossible to series two winding.
    Reply to Post • 

  8. #5
  9. Join Date
    Jun 2015
    Posts
    7
    Reputation
    Thanks ,buddy
    it is battery powered. you are right.I will try it next time.
    Reply to Post • 

  10. #6
  11. Join Date
    Jun 2015
    Posts
    7
    Reputation
    i am young in the testing world but just seen something similar the other day. the senior guys on site came up with that it is possible to have two wingdings in series with certain type of xfmr. they concluded to remove the jumpers that tie the wingdings together which i believe stabilized the results. Just a thought good luck
    Reply to Post • 

  12. #7
  13. Join Date
    Apr 2014
    Location
    DC
    Posts
    12
    Reputation
    This happened to me once. I accidentally put two wingdings in series and my reading doubled.


    Quote Originally Posted by stevenwerynski View Post
    it is possible to have two wingdings in series with certain type of xfmr.
    Reply to Post • 

  14. #8
  15. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    32
    Reputation
    Quote Originally Posted by moon1958moon View Post
    Hi, everyone. I used a winding resistance tester to test 0.75 MVA transformer primary (13800-600). I got a unbalance phase resistance. H1-H2 WAS 2.6om AND H1-H3 WAS 3.8OM. H2-H3 WAS 8.7OM.

    I DON'T THINK SOMETHING WRONG WITH THE TX, IT IS ACCEPTANCE TEST. I USED CPC-100 TO TEST TX AGAIN. I GOT EVERY PHASE WERE AROUND 2.6OM.

    I THINK THE REASON FOR WINDING RESISTANCE IS THAT I DID NOT DISCHARGE THE TX AFTER H1-H2 TESTING AND STARTED TO TEST H1-H3 IMMEDIATELY. BUT THE CPC-100 DISCHARGE THE TX AUTOMATICALLY.

    JUST REMIND TO DISCHARGE THE TX AFTER TEST.
    Reply to Post • 

  16. #9
  17. Join Date
    Apr 2015
    Location
    OH/MI
    Posts
    32
    Reputation
    I use the cpc regularly and the only time I've seen issues like this it's either due to incorrect connection ( 2 windings like previously stated) or just a high resistance at your lead connection point. What current did you test at with which leads?
    Reply to Post • 

Login or register to leave a reply!



Related Topics

  1. winding resistance of power transformers
    By Sanjayo in forum NETA Level 2 Exam
    Replies: 4
    Last Post: March 27, 2016, 07:13 PM
  2. winding resistance tolerance for a transformer test
    By Larry5441 in forum Electrical Testing Talk
    Replies: 6
    Last Post: June 29, 2015, 04:33 PM
  3. Transformer winding resistance, balance ?
    By rgrabis in forum Electrical Testing Talk
    Replies: 2
    Last Post: June 26, 2015, 07:21 PM
  4. Replies: 4
    Last Post: January 24, 2015, 12:34 PM

Tags for this Thread

Search TestGuy
   Tag Cloud   Advanced Search
Follow us


Explore TestGuy


NETA Certification Training


Help and Support