Which is not required for 15kV inline cable splice?

    #1
  1. Join Date
    Dec 2014
    Posts
    84
    Reputation

    Which is not required for 15kV inline cable splice?

    I don't know anything about cable splicing, can someone help me with the question below? If you have a manual or instruction sheet that shows the process could you post it? That would be really helpful. Thanks!

    New installation of 350 MCM copper 15kV tape shielded 100% EPR insulated power cable requires inline splice. To properly perform a splice on this cable which is not required:

    A. Extruded strand must be carried intact across the splice

    B. Both sides have proper stress relief at the point to tape shields are terminated

    C. Properly rated conductor must be used to join the two 350 MCM conductors

    D. Some type of conductors are required to cross splice and connect the shield on both sides

    E. Sufficient amount of the semicon material used as part of the insulation shield must be removed to establish adequate creepage distance on both sided of splice
    Reply to Post • 

  2. #2
  3. Join Date
    Dec 2014
    Posts
    84
    Reputation
    bump, no cable splicers here?
    Reply to Post • 

  4. #3
  5. Join Date
    Jun 2015
    Posts
    7
    Reputation
    i am just learning some basic splices i find it to be fun and different from our every day work.. but sorry no answer for you. i will be checking back with this post to see what you come up with
    Reply to Post • 

  6. #4
  7. Join Date
    Dec 2015
    Posts
    39
    Reputation
    is this question on the neta level 3 test?
    Reply to Post • 

  8. #5
  9. Join Date
    Dec 2014
    Posts
    3
    Reputation
    Quote Originally Posted by Sanjayo View Post
    is this question on the neta level 3 test?
    A. Extruded strand must be carried intact across the splice
    Reply to Post • 

  10. #6
  11. Join Date
    Feb 2016
    Location
    Dallas, TX
    Posts
    1
    Reputation

    Cable Splicing question

    I believe that answer A is the one that does not fit. I am not sure what they mean by an extruded strand?
    Reply to Post • 

  12. #7
  13. Join Date
    Jan 2017
    Location
    Littleton, CO
    Posts
    1
    Reputation

    This questions was not on my NETA III exam, but there's a large question pool.

    This questions was not on my NETA III exam, but there's a large question pool.

    Quote Originally Posted by Sanjayo View Post
    is this question on the neta level 3 test?
    Reply to Post • 

  14. #8
  15. Join Date
    Oct 2015
    Posts
    1
    Reputation
    Cross splicing is a completely separate method of cable splicing. Answers A, B, C, and E are steps within several in line splicing procedures from 3M.
    Reply to Post • 

  16. #9
  17. Join Date
    Apr 2014
    Location
    Houston TX
    Posts
    10
    Reputation
    "A" is the step that isn't used in cable splicing.

    Generally the splice kit is going to use some assortment of a tape spring with a braided conductor to reconnect the ground shield. I would say that answer "D" describes why "A" is wrong.
    Reply to Post • 

Login or register to leave a reply!



Related Topics

  1. Cable hi-pot withstanding time, why 15 minutes?
    By moon1958moon in forum Electrical Testing Talk
    Replies: 28
    Last Post: October 14, 2016, 08:58 AM
  2. Circuit breaker hot spot found without an infrared camera
    By SecondGen in forum Electrical Testing Talk
    Replies: 0
    Last Post: February 5, 2016, 11:05 AM
  3. Cable hi-pot step voltage test
    By cjones09 in forum Electrical Testing Talk
    Replies: 1
    Last Post: August 25, 2015, 06:38 AM
  4. Replies: 0
    Last Post: December 1, 2014, 05:00 AM
  5. Cable Insulation Precentage
    By CanTest in forum Electrical Testing Talk
    Replies: 1
    Last Post: June 24, 2014, 04:21 PM

Tags for this Thread

Search TestGuy
   Tag Cloud   Advanced Search
Follow us


Explore TestGuy


NETA Certification Training


Help and Support